Can't get linearity from 1746-NT4/mV module

Deer

Member
Join Date
Jun 2002
Posts
124
Hi,

I have a problem with my 1746-NT4 thermocouple/Mv module, actually with this module i would like to injected with milivolt injector (0-50 mv), but I can't get linearity value from this module.
Following are sample point using milivolt injector:
mv Injector PLC value
0 mv 435
10 mv 2010
20mv 4000
30mv 4225
40mv 6000
50mv 7345

What happend with it and does any body here have experience with this case?

Rgds,
Deer
 
How do you have the card configured? ( input type, data format )See Pic and PDF

InputTypeConfiguration.jpg
 
Last edited:
I think Mickey has the solution. Thermocouples are not linear so if you have the modules setup for a TC type then you would get a non linear reading when a linear input is applied.
 

Similar Topics

Dear, i was looking at the datasheet for level transmitter from E&H, and they offer 5-point linearity protocol instead of the basic (i guess...
Replies
5
Views
2,976
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
Replies
5
Views
145
I had a 1746-HSCE go suspected bad. have to swap the card in the morning. Other than dip switch settings is there any configuration to do?
Replies
1
Views
1,027
Happy Friday everyone! I recently installed a new module, 1746 NIO4I, into the last slot on this chassis. Got the normal IO mismatch fault, added...
Replies
5
Views
1,575
Does anyone know where to get either new or aftermarket 1746-N3 connectors and cables for SLC 32 point discrete in cards? I have a used MCC that...
Replies
1
Views
1,245
Back
Top Bottom