Can't get linearity from 1746-NT4/mV module
Deer
Jun 2002
124
I have a problem with my 1746-NT4 thermocouple/Mv module, actually with this module i would like to injected with milivolt injector (0-50 mv), but I can't get linearity value from this module.
Following are sample point using milivolt injector:
mv Injector PLC value
0 mv 435
10 mv 2010
20mv 4000
30mv 4225
40mv 6000
50mv 7345
What happend with it and does any body here have experience with this case?
Rgds,
Deer
How do you have the card configured? ( input type, data format )See Pic and PDF
I think Mickey has the solution. Thermocouples are not linear so if you have the modules setup for a TC type then you would get a non linear reading when a linear input is applied.
Dear, i was looking at the datasheet for level transmitter from E&H, and they offer 5-point linearity protocol instead of the basic (i guess...
2,978
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
183
I had a 1746-HSCE go suspected bad. have to swap the card in the morning. Other than dip switch settings is there any configuration to do?
1,028
Happy Friday everyone! I recently installed a new module, 1746 NIO4I, into the last slot on this chassis. Got the normal IO mismatch fault, added...
1,576
Does anyone know where to get either new or aftermarket 1746-N3 connectors and cables for SLC 32 point discrete in cards? I have a used MCC that...
1,248