Hey,
I'm working on a system that is going to be somewhat modular in nature, and Ethernet based, using CompactLogix and Studio 5000. For all my modules I need to have the "Major Fault on Controller if Connection Fails While In Run Mode" enabled, to make sure I don't lose connection to a module I should have communication to.
The issue comes in when they change configurations of the equipment, they may remove some of the modules. They'll have to make the corresponding change in the configuration section of my program when they remove a module so that the program knows it is missing. Now I will want to disable the "Major Fault on Controller if Connection Fails While In Run Mode" function, using logic.
My reseller gave me instructions on how to inhibit the module all together using an SSV, but I'm not sure if inhibiting the module will prevent a major fault from occuring if the module is missing. I won't be able to do any testing until this weekend, so I wanted to ask if anyone would know if inhibiting the module is going to work for what I need it to do, or if there is a SSV command I can use to enable and disable the "Major Fault on Controller if Connection Fails While In Run Mode" selection, depending on configuration.
Thanks!
Great question, and fortunately the answer is Yes !
The two check-boxes on the Connection tab for the I/O modules can be read and written by the same GSV/SSV instruction.
It's the Mode attribute of the Module object.
From the Help file, under "GSV/SSV Objects":
Bit 0 If set, causes a major fault to be generated if any of the MODULE object connections fault while the controller is in Run mode.
Bit 2 If set, causes the MODULE object to enter Inhibited state after shutting down all the connections to the module.
Hey thanks for the help, that's quite simple. I'll just change my software from toggling bit 2, to toggle bit 0 instead. Easy!
Hey,
..... For all my modules I need to have the "Major Fault on Controller if Connection Fails While In Run Mode" enabled, to make sure I don't lose connection to a module I should have communication to.
This does not "make sure you don't lose connection to a module you should have communication to.."
You cannot prevent losing comms, but you can react to it more elegantly than Major-Faulting the controller. Perhaps a more orderly shut-down of your process or machine would be better, at least then you can annunciate the fault ...
Yes, I had poor wording, I know I can't prevent losing comm to a module, if someone unplug a cable not much I can do about it.
Yes you are right I can probably do it more elegantly. How would I go about monitoring the communication status of a module in the logic?
I'm experiencing this error myself right now. For the time being, to get the machine back into production, I just un-checked the major fault tick box and they've been back up and running ever since. Anyone have any idea what CAUSES a module to lose connection to controller in the first place...?
The same things that cause any kind of failure:
* Bubba
* Random equipment failure
* Failure due to external factors (heat, water, Bubba with steam cleaner etc)
* Poor installation practices resulting in your ethernet link either out right failing, or intermittently failing.
I have experienced "losing connection" issues. This was to a ControlNet bridge module in a ControlLogix chassis that had been installed for over 12 years.
I discovered that removing the module from the chassis and replacing it got it working again.
I deduced that the contacts could be dirty or tarnished after all those years. We cleaned all the module's contacts with a quality spray cleaner, and pushed the modules in and out a few times.
Never had the problem again....
I have two identical machines running similar HMI projects, the only difference is one is done in FactoryTalk View Version 10 and the other is...
128
Hoping someone can give me some guidance or confirmation of what I need to do. We have a FactoryTalk SE program that I need to change the IP...
96
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
180
Greetings I have a problem, my system is the following: wincc v8.0 (demo), logo8.3, abb m2m analyzer. I created some pages to display the...
69
We had one go down. we have a new one. Their emergency Number don't work. The Model is TLSA046AAH-330N01-007 A catalog says we need software TET...
172