Good evening, i wanna change a PID loop from a Siemens TP 177 Micro panel
and the PLC is a Siemens s7-226

the value for p, i, d, is stored in
VD6 1.0
VD10 10.0
VD14 0.0
they are floating points
and now i wonder how to set it up right on the panel.
i have bean trying almost everything but cant get it right :angr:
i only gets xxxxx on the panel or the closest is 1 when it should be 1.0
what´s the data type and do i need to scale or what?

Thanks,
 
Working with this settings in wincc:

TAG: real

IO Field:
format type:decimal
format pattern: 99.99
 
Hi there
Help file shows that Ti, Td and Kc are all real, that is you need to use VD.
But you are already using this and is getting XXXX so i guess your HMI is not communicating with PLC, What about the other tags?? are they working O.K?
 
Working with this settings in wincc:

TAG: real

IO Field:
format type:decimal
format pattern: 99.99

it working great with this settings!! 🍻
that i didn't try last time was changing the format pattern to 99.99
 

Similar Topics

Usually I just read other posts on here but I simply cannot find the answer to my problem this time. I have a PLC-5 40E. There is a PID that...
Replies
6
Views
3,023
Hello everyone, In RSlogix5000 PID loops are running in continuous task. Those are to be configured in periodic task and tuning. can anyone...
Replies
14
Views
3,151
I am looking to change a PID loop operation on a ROC Floboss 103. The valve is fail open. they need it to fail close now. Do I need to make the...
Replies
1
Views
1,969
Hello, I changed controller type in RSLogix 500 from SLC 5/02 to MicroLogix 1200 and was given the ladder logic to update it for the new...
Replies
25
Views
4,834
Compactlogix. Newest version of rslogix 5000. Online editing open up PID dialog cant change values. What am i doing wrong or missing? Thank you
Replies
2
Views
1,943
Back
Top Bottom