CIP Path

Stran

Member
Join Date
May 2011
Location
Canada
Posts
14
Hi,
I'm fairly new and was wondering what a CIP path is. I'm currently trying to use the cimquest InGear driver to read tags from AB software
 
Hello,

From our help file:

Path
This is the path to the endpoint (controller). A "-1" value in the path is ignored. The most common path will be 1 - 0. That is from the Ethernet/IP card to the CPU (slot 0). If the CPU was in slot 1 the path would be 1 - 1. All the non used path fields must be -1. If the path is to a CPU in another rack the path would be longer. Please refer to AB documentation for proper path settings.
Example
Rack 1
Slot 0 ControlNet card
Slot 1 CPU
Slot 2 Ethernet/IP card
Rack 2
Slot 0 ControlNet card
Slot 1 CPU
To access the CPU in rack 2 the path would be: 1 - 0 - 2 - 9 - 1 - 1
1 = Ethernet/IP
0 = ControlNet card in Rack 1 slot 0
2 = Channel 1 of ControlNet card
9 = Rack 2
1 = ControlNet card in Rack 2 slot 0
1 = CPU Rack 2 Slot 1
 

Similar Topics

I noticed something that’s mostly just a curiosity. Maybe someone here knows. An IT system is reading a L82 with the on-board IP and 1,0 added...
Replies
2
Views
711
Hi All, In RSLogix 500, under Controller Properties, in the Controller Communications tab, the "CIP Path" is stored for my controller. This path...
Replies
1
Views
1,366
I have a question on a subject of etherent nodes in rslogix 5000 project tree for a project that I am working on. I am trying to read if read...
Replies
5
Views
4,706
Hi, I have to connect a few AB plcs to WinCC.. I usually work with Siemens so I have a problem.. They are connected via ethernet. The driver I...
Replies
7
Views
4,400
Hi, First time poster, long time reader. I've got a mass flow controller device for controlling the flow of gas. It has a flowmeter and an...
Replies
4
Views
296
Back
Top Bottom