Citect 7.2 Limiting Number of Popups

Darkshrimp

Member
Join Date
Mar 2011
Location
WA
Posts
20
Hi all.

We're currently using Citect 7.2 and recently noticed it is limiting the number of pop ups to 3.

Is there a setting in the ini file I can change to remove this limitation?

Thank you.
 
That is set in the ini file - do not allow too many pop ups as the operator becomes confused and the computer/application kind of struggles. I normally limit pop ups to 3.
 
window limits

Open Computer Setup Editor (under Tools menu) and on the right side window go to the Page Parameters. The item you want is the Windows one. This sets the number of simultaneous windows that can be open (we have ours set to 11). This parameter can be set in the citect.ini file, or included in the project itself under System/Parameters.
 
....addition to the previous post: We have ours set to 11 Windows because this included ALL windows, including process graphics pages and equipment operation small pop ups (Super Genies). So we think that someone might have 3-4 process pages open, and might want to have open 5-7 Process Variable or Equipment Control popups at the same time.....
 

Similar Topics

So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
50
Hello, i've been at this for months now, i tried creating accounts on the aveva website but it seems to never approve my accounts or at least when...
Replies
3
Views
74
Hello, I have a running project on Citect v5.42 and simatic net v6.4 I have created a new spare PC and loaded all software like Citect, station...
Replies
0
Views
73
Hello everyone, In a factory where we installed Citect 7.20 the computer began to show the first signs of end of life. They never considered...
Replies
0
Views
76
I have a running backup of Citect and plc and I want to make a spare PC station so I have installed the win XP and somatic net v6.0 and import the...
Replies
3
Views
125
Back
Top Bottom