citect cviba

toineke34

Member
Join Date
Dec 2007
Location
peer
Posts
1
hello iam using citect together with a modbus driver. if i want to select bits this is not possible. digital is reading from a different adres then my machine is providing. i can only see a compleet word in the 40000 range not in the 10000 range i tried to write something in citect vba but how to us this file or is there a simpler way

greetings antoine
 
have you tried addressing your digital IO as 40000.x where x is 1 to 16. You may be able to address individual bits as 40000.1 etc. If you cannot do this or if this does not suit You may want to check Citec's help about Remapping.
 