Hello,
Some variables in an old Citect program (V5.42) are hash comms. After some investigation, I have noticed that they are not looking at the PLC but a hard disk file:-
Here are a selection of the variables from variables.dbf:-
ADDR RAW_ZERO RAW_FULL ENG_ZERO ENG_FULL ENG_UNITS FORMAT COMMENT
Disp_Time_Cycl1 INT HardDisk I0400 0 2359 0 2359 #### B1C1 start time reminder.
Disp_Time_Cycl2 INT HardDisk I0401 0 2359 0 2359 #### b1c2 reminder start time
Units.DBF:-
SERVER NAME NUMBER ADDR PROTOCOL PORT
IOSERVER PLC 1 100.100.100.2 KOYONET205 PORT1_BOARD1
IOServer HardDisk 2 [tags]:Harddisk.dsk GENERIC DISKDRV
IOServer Alarm_Devices 3 ALARM ALARM
The Harddisk.dsk file was lost when the Scada PC crashed.
You can see the variables are just reminder times.
How/where do I create the Harddisk.dsk file and anyone know the format of how I will populate the variables in there for Citect to read instead of displaying hash comms?
Thanks for any help
Matt
This is a PLC on the hard disk I believe. It should have been saved in the backup.
Have a look in Citect help for the PLC on the hard disk.
I think it is called 'disk PLC' or something similar.
Hi Matt,
Sounds like the "Harddisk.dsk" file has not created it self when Citect was first started on your new PC. I'd say the reason for this is that there is a path substitution shown in your post called [tags]. In older versions of Citect the folders associated with the path were not automatically generated, you would have to create them first. Path substitution is normally defined within the Citect.ini file, but it sounds like that has been lost too.
Look up path substitution in the Citect help and you will see how to create a substitution for [tags].
Hope this helps.
Andy
Thanks Bob and Andy
Andy - that was it!
I searched on Substitution and put a full path in
c:\citect_PLC\Harddisk.dsk instead of the substitute [tags]:Harddisk.dsk as tags substitute wasnt in the citect.ini
The harddisk.dsk was recreated when I ran the project and no longer hash comms but variables I can read and write.
Thanks Heaps Andy
Regards
Matt
This is a Citect SCADA question I have Six variables of type REAL (Float) to compare and determine (identify) which variable has the highest...
1,422
Can anyone help me out with where the file for the citect disk variables is kept? I have a variable tag "email_reception" on device"disk" at...
2,488
Hello I created a program in unity pro and HMI local on Vijeo Citect and communication between them realize by OFS OPC FACTORY . before the...
1,949
Is there any way to access the disk I/O variables in citect V5.5, there is one tag available in the variables.dbf and it is defined as disk I/O...
1,774
I've got Siemens S7300 PLC connected to Citect PC via Ethrnet. INT and Bool values are written and red without problems but as for Real values...
3,237