Click PLC to Studio 5000 via Ethernet

forqnc

Lifetime Supporting Member
Join Date
Jul 2009
Location
Elizabeth City
Posts
148
Hi,
I just successfully set up a Click PLC as remote I/O to a CompactLogic PLC. Everything is working but when monitoring an Analogue value it is split into 4 - 8 bit registers. Just getting my feet wet in Studio 5000, I have tried COP, FLL and even ADD instructions to combine the data in Studio, but I do no get accurate results. This same question was posted on the YouTube site by someone else with no response.
Any assistance is appreciated.
 
Thank you Ken, I'd used 4 previously thinking I needed 4 bytes, changed to 1 as you suggested and works great.
Thanks again.
 