I don't have a lot of experience with Studio5000, years with SLC's and PLC5's and started on PLC2's.
My present new project is a 1756-L73 using Studio500 v33. The 10 slot rack has 2 fast analog in/out cards - 4 in 2 out each. 1756-IF4XOF2F, Ser A Rev 1.001
Still on the bench programming and testing, but I have a big problem with the analog inputs, I have not tested the outputs yet.
With a signal from signal conditioners and the mA monitored with a calibrator the mA to the inputs is consistent and may only fluctuate 0.02 mA at the most, however online with the CPU running the it runs wild. The inputs are set to range from 0 to 20000, I have a scaling AOI and added a dampening AOI.
With the mA input staying the same, if the scaling changes it to temperature from 32 to 212°F the temperature should stay at 75°. However, even with dampening, the 75 drops to as low as 36, up to 60, down to 40, up to 75, down to 42, etc. It never goes over 75, and never drops to 32 or below.
EDIT: the raw inputs from the analog cards fluctuate, not caused by the Scaling AOI.
I have double checked the wiring per the manual and moved the input to the other card and other inputs.
On the module configs I have: (for all 8 inputs)
RTS: 2.00 ms
Synchronize Module Inputs NOT checked
Input Type: Current (mA)
Input Range: 0mA to 20mA
High Signal: 20.0000
Low Signal: 0.0000
High Engineering: 20000.000
Low Engineering: 0.0000
Digital Filter: 0.00 ms
Is it possible I have some setting wrong? Is there a default setting I haven't changed?
My present new project is a 1756-L73 using Studio500 v33. The 10 slot rack has 2 fast analog in/out cards - 4 in 2 out each. 1756-IF4XOF2F, Ser A Rev 1.001
Still on the bench programming and testing, but I have a big problem with the analog inputs, I have not tested the outputs yet.
With a signal from signal conditioners and the mA monitored with a calibrator the mA to the inputs is consistent and may only fluctuate 0.02 mA at the most, however online with the CPU running the it runs wild. The inputs are set to range from 0 to 20000, I have a scaling AOI and added a dampening AOI.
With the mA input staying the same, if the scaling changes it to temperature from 32 to 212°F the temperature should stay at 75°. However, even with dampening, the 75 drops to as low as 36, up to 60, down to 40, up to 75, down to 42, etc. It never goes over 75, and never drops to 32 or below.
EDIT: the raw inputs from the analog cards fluctuate, not caused by the Scaling AOI.
I have double checked the wiring per the manual and moved the input to the other card and other inputs.
On the module configs I have: (for all 8 inputs)
RTS: 2.00 ms
Synchronize Module Inputs NOT checked
Input Type: Current (mA)
Input Range: 0mA to 20mA
High Signal: 20.0000
Low Signal: 0.0000
High Engineering: 20000.000
Low Engineering: 0.0000
Digital Filter: 0.00 ms
Is it possible I have some setting wrong? Is there a default setting I haven't changed?