Code Review - best practice for sequential execution control
Jun 2016
Boston, MA
Could experienced PLC programmer take a look at these lines of code? It is for controlling a stepper servo motor, as you will see some familiar motor commands. This code is intended for a Panasonic FP-x plc, so there are some FP specific elements, such as R904A=1 flag being COM2 ready, F7_MV2 for moving two words into a dword, and the mess needed to call MODBUS send (F145_SEND) and receive (F146_RECV).
Mainly, I am wondering if the structure I am using to control sequential MODBUS communications are as efficient (in writing style, as well as execution) as they can be. For example, the DF(X1) actions would ideally be:
if(DF(X1)) then
setSpeedAcceleration(10,10,200);
setFeedDistance(1000);
motorFeedToDistance();
while (readMotorCompleteStatus = false);
end_if
and the DF(X2) would be:
if(DF(X2)) then
setDirection(-1);
setHome();
motorSeekHome();
zeroEncoderCount();
zeroPosition();
end_if
But it seems I need to separate each MODBUS communicating step into individual ladder rungs. Please let me know if there are smarter ways to do the same thing shown here.
if (DF(X1)) then
(* set speed and accel, do a feed cmd, and read status for complete *)
seq_feed := TRUE;
tms_readStatusDone :=FALSE;
tms_feedDone :=FALSE;
tms_setSpeed:=TRUE;
tms_setSpeedDone :=FALSE;
end_if;
if (DF(tms_setSpeedDone)) then
tms_feed:=TRUE;
end_if;
if (DF(tms_feedDone)) then
tms_readStatus:=TRUE;
seq_feed := FALSE;
end_if;
IF (tms_setSpeed) THEN
DT110:=20; //acceleration of 20
DT111:=20; //deacceleration of 20
DT112:=100; //speed of 100
DT113:=0; //higher byte of move distance
DT114:=distance; //lower byte of move distance
F7_MV2(s1 := 16#5, s2 := 16#2001, d => controlword);
IF (R904A) THEN
F145_SEND(s1_Control := controlword,
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 27); //address to put all 5 words
tms_setSpeed := FALSE;
tms_setSpeedDone :=TRUE;
end_IF;
end_IF;
IF (tms_feed) THEN
DT110:=16#66; //cmd 66 is feed to distance
F7_MV2(s1 := 16#1, s2 := 16#2001, d => controlword);
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 124);
tms_feed := FALSE;
tms_feedDone := TRUE;
end_IF;
end_IF;
IF (tms_readStatus) THEN
IF (R904A) THEN
F146_RECV(s1_Control := controlword,
s2_AdrType := DT0,
s2_AdrOffs := 1, (* 40002 for SC status code *)
d_Start := datafromtsm);
(* tms_readStatus := FALSE; *)
if (datafromtsm = 16#9) then //9 means motor move done
(* motor is in position and enabled *)
tms_readStatusDone := TRUE;
end_if;
end_IF;
end_IF;
if (DF(X2)) then
(* call Seek Home *)
seq_seekHome:=TRUE;
tms_setDir := TRUE;
tms_setDirDone:=FALSE;
end_if;
if (tms_setDirDone) then
tms_setHome:=TRUE;
tms_setHomeDone :=FALSE;
end_if;
if (tms_setHomeDone) then
tms_setHomeDone:=FALSE;
tms_seekHome:=TRUE;
tms_seekHomeDone :=FALSE;
end_if;
tms_seekHome:=TRUE;
end_if;
if (tms_seekHomeDone) then
end_if;
if (tms_readStatusDone AND seq_seekHome) then
tms_zero126:=TRUE;
tms_zero126Done:=FALSE;
end_if;
if (tms_zero126Done) then
tms_resetEncoder:=TRUE;
tms_resetEncoderDone :=FALSE;
end_if;
if (tms_resetEncoderDone) then
tms_resetEncoderDone:=FALSE;
tms_resetPosition:=TRUE;
tms_resetPositionDone :=FALSE;
seq_seekHome :=FALSE;
end_if;
IF (tms_setDir) THEN
DT110:=16#FF;
DT111:=16#FF;
F7_MV2(s1 := 16#2, s2 := 16#2001, d => controlword);
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 30);
tms_setDir := FALSE;
tms_setDirDone :=TRUE;
end_IF;
end_IF;
IF (tms_setHome) THEN
DT110:=16#35;
DT111:=16#4C;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 125);
tms_setHome := FALSE;
tms_setHomeDone :=TRUE;
end_IF;
end_IF;
IF (tms_seekHome) THEN
DT110:=16#6E;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 124);
tms_seekHome := FALSE;
tms_seekHomeDone := TRUE;
end_IF;
end_IF;
IF (tms_zero126) THEN
DT110:=16#0;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 125);
tms_zero126 := FALSE;
tms_zero126Done := TRUE;
end_IF;
end_IF;
IF (tms_resetEncoder) THEN
DT110:=16#98;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 124);
tms_resetEncoder := FALSE;
tms_resetEncoderDone := TRUE;
end_IF;
end_IF;
IF (tms_resetPosition) THEN
DT110:=16#A5;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 124);
tms_resetPosition := FALSE;
tms_resetPositionDone := TRUE;
end_IF;
end_IF;
You're on your way but there are some minor things you need to fix.
I suggest using an integer to keep track of what you are doing instead of a bunch of flags (booleans). The flags are never active at the same time while an integer can only have one value at the time. Integer is easier to check, easier to set to any value and easier to debug (only one thing to look at).
My preference is to use a case statement instead of a bunch of if statements. Check my post in your other thread.
The code were you read the status wont work. You need to do the RECV statement first THEN wait for it to complete (R904A) and then check whatever status you received to know if you're done or not.
You also need to check for errors if you have any and determine what to do with them.
Always figure that you need to be able to pull the plug on the communication at any time (or cycle power on the drive) and the communication should resume in a meaningful way, no matter what you were doing in your program.
Revised code for review - with case and int for state control
Pete.S: Thank you for your very constructive comments, I love the ideas you suggested. I have implemented some of the ideas you mentioned (minus error checking.. I will work on that tomorrow.) The revised code is below. Should I consider encapsulating the repetitive part of the code (IF (R904A)....) in a function or function block?
(* state_feed:=0; *)
(* state_home = 0; *)
CASE state_feed OF
0: (*do nothing, idle*)
state_feed :=0;
1: (* start sequence *)
DT110:=20;
DT111:=20;
DT112:=100;
DT113:=0;
DT114:=distance;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 27);
state_feed := 10;
end_IF;
10: (* execute feed command *)
DT110:=16#66;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 124);
state_feed :=20;
end_IF;
20: (* check status until feed is complete *)
IF (R904A) THEN
s2_AdrType := DT0,
state_feed :=21;
end_IF;
21: (* check status read data *)
IF(datafromtsm = 16#9) THEN
state_feed := 999;
ELSE
state_feed := 20;
end_IF;
999: (* squence complete *)
state_feed = 999;
ELSE (* catch unspecified states *)
state_feed = 888;
END_CASE;
case state_home of
state_home :=0;
1: (* start sequence - set DI direction*)
DT110:=16#FF;
DT111:=16#FF;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 30);
state_home :=10;
end_IF;
10: (* Set seek home parameters *)
DT110:=16#35;
DT111:=16#4C;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 125);
state_home := 20;
end_IF;
20: (* execute seek home command *)
DT110:=16#6E;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 124);
state_home :=30;
end_IF;
30: (* check status until feed is complete *)
IF (R904A) THEN
s2_AdrType := DT0,
state_feed :=31;
end_IF;
31: (* check status read data *)
state_feed := 40;
ELSE
state_feed := 30;
end_IF;
40: (* prepare register 126 for zero encoder and position *)
DT110:=16#0;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 125);
state_home := 50;
end_IF;
50: (* reset encoder count to 0 *)
DT110:=16#98;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 124);
state_home := 60;
end_IF;
60: (* reset position count to 0 *)
DT110:=16#A5;
IF (R904A) THEN
s2_Start := DT110,
d_AdrType := DT0,
d_AdrOffs := 124);
state_home := 999;
end_IF;
999: (* sequence complete *)
state_home := 999;
state_home := 888;
END_CASE;
Maybe you should. I'm not sure I would though. But if you can make the code more compact it's often easier to read.
It's generally better to format the code for clarity than it is to always follow a set of fixed rules.
A couple of things you do over many lines I would just do in one.
The important thing for each state is:
  • What is this state doing?
  • Where does it go when it's ready?
The first thing is the comment and the second thing is setting the state at the end. Those should be on their own lines.
But the rest could be written more compact. Unfortunately ST forces you to write the name of the parameters your passing to a function so that makes the code a bit heavy handed compared to regular programming languages.
Now you made two state machine but only one can run at the time since they are communicating with the same driver. So I would put them together. Put the homing section starting at 100 or something.
If you wanted to you could have the state machine start itself by checking your the start condition and then going to the next state. So in the first state you would check if you should do any homing (in that case goto 100) or if you do the other (goto 2 or whatever).
I still like to keep 0 as my "do nothing at all" because sometime you want to be able to turn something completely off.
I prefer to use variables (constants) as step numbers. Instead of using 0, 1, 100, 200 etc.
That way you can count your steps 0, 1, 2 , 3, 4 and if you need to add a step, you can just move them all down with a copy paste command in the definition of the constants.
I usually use unsigned short integers for steps (max 255). Rarely do I need more than 255 steps but if I do, I can just change the definition quickly anyway.
That's some good points.
For really large sequences I usually expand into two variables to track where I am, a step and a sub step. I write them like this in the documentation: 1.1, 1.2, 35.3 etc.
Regarding the use of bytes I'm not sure that you will gain any performance by going short int. If the PLC is 16 bit internally and I think they are at least 16 or more likely 32, its faster to use a 16 bit integer than 8 bit.
Hey guys, I've recently been asked to review some code at a water treatment plant that isn't working right; seems like sometimes it'll work, but...
5,258
260
hello, I'm a student and for my final grade I have to repare a sepro robot. the only problem I have for now is that i have an error code 3...
37
I received an email from a student with the following code attached. This is supposed to control a floodgate system, and supposed to be written...
23
788
I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
204