So I installed release 1.09.003
So... is it working? Or do you still have to test?
So I installed release 1.09.003
Has this been working before, or is it the first time for you with Citect and S7-1500 ?
If this the first time, then I can imagine a few things that you must be aware of.
I doubt that Citect can read S7-1500 addresses symbolically (I might be wrong).
If I am correct, then you must setup each tag with absolute address access.
And, the accessed variables in S7-1500 must be set to non-optimized.
And, PUT/GET access must be enabled on the S7-1500 - default is not enabled.
When setting up the connection, it is basically the same as for S7-300, except that the rack/slot which was always 0/2 in S7-300 is always 0/1 in S7-1500.
If the S7-1500 has enabled PUT/GET, and the tags are accessed with absolute addresses, then it is exactly as for an S7-300 - except for the rack/slot.
So even legacy software that knows nothing about S7-1500 should work as long as it did work with S7-300.
edit: I studied the help pages, and it seems that for S7-1500 the only thing you must specify is the IP address. So the rack/slot is probably implied for S7-1500.
Any help pages for the setup of the tags ?
The whole point of the S7TCP driver is to read/write addresses symbolically. I managed to get the older PSDIRECT driver working with the S7-1500 using PLCSIM Advanced V2.0 SP1 (originally it worked with S7-300), and in this case I had to set to non-optimized using absolute addresses.
No. It's only used with the PSDIRECT driver only. No "middleman" with the S7TCP.Do I have to use PSDirect as middleman to use S7TCP driver?
Yes.If I to use PSDirect then I have to use absolute addresses, is it?
No it is not working. I get the warming message saying it is not the final release or need license. Here is the image.
I managed to get the older PSDIRECT driver working with the S7-1500 using PLCSIM Advanced V2.0 SP1 (originally it worked with S7-300)
No, I have no experience with Citect (except 20 years ago, and that was with an AB PLC).ZamkuD said:When you say basically it is same as S7-300, you mean use S7NT driver?
I didnt say anything about that. But I do know that Citect supports various alternative ways to communicate with Siemens, amongst these are Simatic Net (S7API driver) or OPC.ZamkuD said:So, you have to use middleware like SImatic Net or PSDirect software to talk to S7-300 CPU. So DO I need to configure any middleman software to configure it.
ZamkuD said:Do I have to use PSDirect as middleman to use S7TCP driver?
Wow, that is confusing. The "direct" driver is actually not direct but requires a middleman.No. It's only used with the PSDIRECT driver only. No "middleman" with the S7TCP.
Wow, that is confusing. The "direct" driver is actually not direct but requires a middleman.
How you simulated using PLCSIM? Maybe I can try that and see if it is working. Then I at least know that driver is working.