Hello,
i need some help!!
i connected both via rs-485 by lan cable.
HMI PLC
RJ-45 Mini Din 8 pin
pin4 A <---> pin1 A
pin5 B <---> pin2 B
pin8 SG <---> pin7 0V
PLC : I config in Twidosuite(Descrobe) to 19200 8 E 1 tried other baud rate too.
HMI : I config in IO Manager --> ModbusRTU01[Com2] to 19200 8 E 1 and ModbusEquipment1 to address 1(PLC)
but when i power on i get msg on HMI display "No reply from PLC within Timeout period. (ModbusEquipment01)"
i need config more? i missed something?
please help!!! or give some instruction.
Thank you.
 HMI              PLC
pin4 A <---> pin1 A
pin5 B <---> pin2 B
I am not familiar with this HMI or PLC, but I would expect the wiring to be A <---> B and B <---> A (like a crossover cable), not A <---> A and B <---> B. I would try swapping the wires on one end.
-Eric
If your using 485 then it does not crossover, so your original cable looks correct. But RS485 requires termination resistors (120 ohm) at the end of each cable.
Make sure both the plc and hmi are set to RTU mode
You are using port1 (programming port)?
If so then you also need to connect pin 5 to 7 (DPT to 0 VDC) on minidin connector. Port1 is on programming mode if you only connect A and B pins. (unitelway protocol I think).
Connecting pin 5 to 0 VDC forces port to use parameters given on port1 configuration.
Port2 uses allways parameters from configuration.
I am trying to setup communications between an m580 and a compactlogix plc. I have confirmed my set up on schneider side is correct and now I am...
3,029
hello everyone we work on a water station using plc schneider M340 and we should make a communication with a dcs honeywell , this dcs should read...
1,318
Hi Guys, I have a Beckhoff CP6607. It has 2 ethernet ports, 2 usb ports, and a serial port. I am trying to connect it to a Scheider VSD, an...
3,989
I want to establish communication communication between Schneider 140 NOC 771 01 and PowerFlex 755 over Ethernet/IP. If anybody have tried this...
4,524
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
154