Just was wondering if there was a way to write something in the program to recognize when the RS-232 communication is not working between PLC to Port Splitter, then to modem and HMI. It seems to work fine when we poll a little Data from PLC but if we start to pull alot more information via Modem for Scada, it tends to freeze the Port splitter. PLC is running still but would like to detect when RS-232 fails to POrt splitter.
You could set up a Scada heartbeat bit in processor memory. The Scada system would be responsibility for setting and clearing this bit periodically and the SLC would have timers monitoring the state of the bit. If communications break down, the bit won't change state and a monitoring timer would finish and set the fault.
I am not familiar with the port splitter, but you might be able to monitor the comms active status (S:33/4) bit in the PLC to detect when it stays off for a significant period of time.
I am not certain that it will go off, but I suppose you could test it.
As for the heartbeat logic, there are a couple of ways to do it. One example:
The HMI monitors B3/0 and sets B3/1 to match it. If B3/0 does not change states within 5 seconds, a comms alarm is set.
The PLC monitors B3/1 and sets B3/0 to the opposite state. If B3/1 does not change states within 5 seconds, a comms alarm bit is set.
Both bits should "flicker" at a pretty quick rate when everything is working normally.
Another method:
The HMI monitors N7:0 and sets N7:1 to match.
In the PLC, if N7:1<32767. Add 1 to N7:1 and write the result to N7:0. If N7:1>=32767, CLR N7:0.
I like the second method, since it makes it easier to "see" the rate of communication, and identify aberrations.
Paul
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
229
Hello guys , im new at plc. i have a few questions hopefully someone can help me out. i extracted from an old panelview550 a pba file and...
1,486
PLC L30ER V30.01 VFD PF 525 V7.0001 Running into an issue that I've never seen before. Ive configured many PF525's before so i know the...
1,250
Hi all, I have been having a frustrating time communicating between my esmart04 HMI and my Productivity P1-540 PLC. Currently, I am simply just...
1,893
Hi All, At site, there is a Pro-Face 19” screen Model: SP-5800WP FWXGA complete with PFXSP5B10 box. Connected via Ethernet to the screen...
3,181