Communication Protocol
hackj0632
Jul 2009
wi
33
Hey guys,
i have a project that i am using a micrologix 1400 on and i have 2 devices
sure servo amplifier and a SCF AC Tech VFD.
the issue seems to be that i want to communicate with channel 0 at 19200 baud rate to servo drive and the VFD is limited to 9600 baud rate.
a few questions i would like advice on are,
1) is channel 2 capable of mod-bus master RS485?
the ML1400 user manual says channel 2 is RS232 only?
RSLogix says i can use mod-bus RTU master or DH-485 so would this be theoretically possible?
if channel 2 is RS 232 only my fall back plan is to change the servo drive to match VFD settings.
thanks in advanced
You and the User Manual are both correct; Channel 2 on the MicroLogix 1400 is an RS-232 port only.
Channel 2 is capable of several different protocols, including Modbus RTU Master. To connect it to a Modbus RTU network that uses RS-485 signalling, you will need an RS-232 to RS-485 signal converter. B&B Electronics is my favorite vendor for those types of devices.
Channel 0 on the MicroLogix 1100 and 1400 controllers has both RS-232 and RS-485 pins; you change the Handshaking mode to determine which ones are active, and choose your cable (1761-CBL-PM02 or 1763-NC01) to connect to the desired pins.
If you don't need the serial ports on the MicroLogix for other purposes, I would say connect the two different devices to the two different serial ports. I think that would tend to reduce the chance of conflict or confusion.
Dear Experts , I have a system which contains 10 PLCs (1214C CPU) each PLC with GSM module (Teltonika RUT955) and 2 SCADA PCs at different...
826
I have been asked to design a control system of which will have 24 winder stations. Each winder station will have its own control system of wich...
1,939
Hello there, I am new to OMRON PLCs so need some help to communicate two PLC over FINS Protocol. Here are the description of the system...
1,046
Dear All, I want to communicate with Arburg Selogica controller v3.09 of an old Arburg injection molding machine. The protocol by which this...
2,625
Hi, I am working on the project that needs to communicate with FX1N PLC by serial port protocol from PC. I am using USB-SC09-FX cable to connect...
2,731