Communication-Signal transmission -1.5kM - Better option

Selk

Member
Join Date
Aug 2019
Location
Dammam
Posts
2
I am looking for a method which transmit OPEN/CLOSE signal from "A" Pump Station to "B" Pump Station.

(a) There is no wire connection between two Pump Stations, 1.5km apart.
(b) Ordinary wireless device is prohibited to use.
(c) Mobile telephones work at both Pump Stations.
(d) Internet service is not available at both Pump Stations, but probably set up newly if required.

Thank you!
 
Is there a PLC or RTU capable of communications at both ends? If so, using a radio modem to set up communications is one option. For 1.5km you might be able to use the Schneider Trio JR900 series licence free model, depends on local obstructions and radio spectrum licensing in your country.

If thats a bit over kill, take a look at Elpro wireless I/O
 

Similar Topics

Hello folks, Hope everyone is doing well. I am a beginner at working in analog signals with PLC Analog module: 1769-IF4 ( 4 analog inputs ) PLC...
Replies
9
Views
1,363
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
0
Views
33
Hi all. I have a Modbus ProSoft module in my setup with a capability of 30 clients (0-29), which I'm trying to monitor the Ethernet Connection...
Replies
0
Views
34
Hi folks, I have a Controllogix in communication with a zigbee coordinator using Logix AIO for modbus tcp. This zigbee coordinator have 3 slaves...
Replies
6
Views
179
Hello, i am using profibus as communication between plc and fanuc arm. I can easily send inputs from plc to arm, but i can't monitor any outputs...
Replies
0
Views
46
Back
Top Bottom