Hi All:
I am having trouble finding out if a A-B Flex I/O is communicating its analog signal through a twisted shielded pair wire to an A-B scanner card.
I checked the wire and found a resistance of 8 ohms between conductors which were tied together at one end about 650 feet away.
I checked for voltage at the connectors with the wires connected and had + 0.068 volts.
The problem is, I am getting my digital signal but not the analog signal. The analog module was replaced and its still not working. The only thing is that the scanner card has not been changed. Could that be it?
Anyway I need some advice on how to check this type of communications between PLC's.
You help will be most apreciated.
Thanks
Joe