I tried flashing a L32E processor to VER. 20 this morining using a compact flash card which i have used on other processors with no issues. However this time i can not seem to talk to the PLC at all. I can set my driver up in RSLinx for the serial port and the AutoConfig is successful. but i can not see the processor in RSWho
The MS and NS lights are solid RED
Any sugestions
You may have already looked at this, but if not...
From the User Manual:
MS = Module Status
The controller is holding the port in reset or the controller has faulted.
1. Clear the controller fault.
2. If the fault will not clear, replace the controller.
The port is performing its power-up self test. Normal operation - No action is required.
A nonrecoverable fault has occurred.
1. Cycle power to the controller.
NS = Network Status
The port has detected that the assigned IP address is already in use.
Verify that all IP addresses are unique.
Been seeing a high failure rate on these PLC's on 2 of our process. The control power is feed through a APC UPS to a 24VDC power supply to power...
4,040
Hello. I am trying to figure out how to setup a PID in Control Logix 1769 Controller in a way that it would control a drive speed by sending...
1,629
Hello guys, I need to add in a few discrete and analog cards for an existing 1769 Compact Logix system at a local Treatment Plant for an...
3,702
Hello Everyone, First of all, I would like to thank you for everyone who helped me in the previous post and this platform is really helpful for...
3,197
I am using ab 1769-l30er for redundancy logic, the secondary controller is not being recognized, the icon is replaced by a yellow question mark...
1,946