I have a problem that's cropped up in the last few days with a controller faulting on a I/O Connection timeout error 03 16
When I look at the major fault in RSlogix 5000 it shows the following
Port: Backplane
Module: $05e5a9a5$
Error: Connection timed out
Info: <None>
After some onsite testing I cannot figure out which module is causing the fault, when I try and replicate the fault by removing the various I/O modules I only can come up with the Module being $07......$ depending on the module that faults out. I for the life of me can not find anywhere on the Rockwell support site find any correlation to the module number and an actual module type.
Can anyone point me in the correct direction?
Thanks!
Just a WAG.....but check that your end cap is not damaged and that it is seated correctly at the end of your I/O.
It has been a while but I remember having some issues with that at one point.
I can't remember what the exact fault was at that time though.
Good luck,
BCS
Hey, so we checked each of the modules, including the cap, and they didn't appear to be damaged. Upon clearing the fault, it does seem to work for a while, but something is definitely having trouble. (I work with Andrew_W)
If you go online with the controller using RSLinx and go to the controller’s I/O tree it should tell you which module has the error.
Hello Dear users, I am writing about a problem that has been bothering me for a few days, i.e. I am trying to establish remote access to the Allen...
96
Hello I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact...
251
Hello, I want to monitor Wonderware historian's heartbeat and trigger a fault if Historian is not communicating /offline in PLC. Currently my...
796
I would like to connect the compactlogic PLC to our network through the A2 port to enable cloud datalogging, but concerned about potential...
1,511
Looking for AOI for Allen Bradley CompacLogix PAC for Statistical Process Control, SPC Functions like XBar, RBar,Average,etc: yakyak:
1,279