Compactlogix and devicenet
joaco1993
Sep 2014
newyork
237
Hi everyone,
Im changing an old 1769L35E PLC and 1769-SDN/B DNET module with a newer 1769L33ER and a new 1769-SDN module.
My question is.. I might have trouble with the device net network ?? As i am going to put a newer SDN module.
Anoter question. If I only change the PLC, can I put the new PLC with the old SDN module ?? Or it might be too old the SDN for the L33ER PLC ?? how can I figure that out
One more. Should I be aware of the firmware I download to the new PLC regarding the firmware the SDN has ??
I mean is the same If I download firmware V20 or V30 to the PLC, the SDN will work with both ?? Or they are correlated ??
Thanks!
Do you have RSnetworx for DeviceNet? Helps to back up the SDN module and download to the new one if you need to. I would first try using the old one, it will have the scan configuration.
We refurbish tube end formers and benders. I'm currently working on an Addison TEF. It has a 1769-L32E with a 1769-SDN DeviceNet scanner (see...
1,648
Hello Mates, first time developing with deviceNet, Im more used with S7 CPUs. My system is a L23E CPU + PanelView 550 on devicenet. I can't...
767
All Found myself in a situation where I need to flash the 1769_sdn Devicenet module from 2.002 to 4.004. I uploaded from the module but it has...
2,396
Dear All, I was getting serious issue with Compactlogix L43 Chassis Backplane mounted DeviCeNet 1769 Scanner Card loosing the DeviceNet files...
2,244
Hello Allen Bradley Experts. I have questions about updating the firmware for a CompactLogix 1769-L23E-QB1 Controller with Firmware version 18 to...
5,151