Compactlogix as time master.
Mikemator
Jul 2013
Durban
36
Hi All.
I have been asked to add some timers and make some simple logic changes to a Compactlogix 5370 series plc, however when I went to download the changes a warning came up about Compactlogix being the master time control for system and third party devices.
The plc controls several vfd's and remote I/O via ethernet/IP and uses a switch to distribute the signals.
What ramifications would there be if I downloaded these changes and how would I rectify them.
Thanks in advance for any help.
Not particularly sure if it would pertain to you. I have only seen the master time controller used with CIP motion (servos).
May be other use cases.
It is possibly only warning you that the plc is the time master and any devices connected to it may lose “time” on a running system.
I would just shut the machine down to a stop and place the plc in program mode. Then download the changes. Should be fine.
Hi Seth.
Thank you for the prompt response. You have confirmed exactly what I was thinking.
It's so great having this forum to bounce ideas off other people.
Thanks again!
Is there a master clock or timer in a CompactLogix that could be used in ladder logic? For example: poll the clock at some event, and add a...
5,273
Hello ********, I have gone thru ModbusMaster.acd sample for compactlogix but unable to make headway. I also read its pdf help. I have experience...
4,817
I have a CompactLogix L23E as a modbus slave being polled by another device (who is the master). However, now I need the L23E to read in values...
5,556
Hi All, Has anyone had experience with the Hilscher DPM Profibus Scanner for AB Compactlogix? I am attempting to use one to add a Profibus...
4,781
Hi, I'm trying to communicate between a CompactLogix L32E and a power transmitter using Modbus RTU. I use a 1761-NET-AIC. Has anyone ever used...
20
15,475