CompactLogix L23E + 485: cable wiring?
Aug 2007
Saint Augustine, FL
178
I have an existing mixed-device 485 modbus network, onto which a CompactLogix L23E is to be added. The network is a 2-wire setup, but all the wiring diagrams I've found for the L23E have indicated the need for additional wires, strangely resembling RS-232.
I've seen dozens of mentions on the net that the serial port on the L23E is Modbus capable (via logic) and supports DH-485, but can't get to the How of this puzzle.
Your confusion is probably coming from the term "DH-485", which is not the same as "RS-485".
Data Highway 485 is an Allen-Bradley proprietary protocol that was used by the SLC-500 family of controllers starting in the late 1980s. Physically, the trunklines of DH485 used 2-wire differential serial signalling with an isolated common conductor, which conformed to the EIA's RS-485 standard.
The DH485 protocol can also be implemented on an EIA-232 serial port, and MicroLogix and SLC-5/0x controllers started doing this in about 1995. The ControlLogix and CompactLogix family controllers also implemented DH485 protocol on their RS-232 serial ports later.
All ControlLogix and CompactLogix serial ports are RS-232 only. Multiple protocols can be implemented on those ports; DF1 full and half duplex, ASCII, Modbus, and DH-485.
It is very common to connect an RS-232/RS485 isolator and converter to a ControlLogix or CompactLogix. The Allen-Bradley 1761-NET-AIC is my default, but I like the DIN-rail mounted ones from B&B Electronics a lot for non-AB connections.
A slightly-related note:
The MicroLogix 1100 and 1400 controllers have an isolated 2-wire RS-485 port implemented in the 8-pin Mini-DIN serial connector along with the normal RS-232 pins. These pins are usually connected using the 1763-NC01 cable that gives you screw terminations.
This RS-485 port can be used for any half-duplex connection that the controller supports, including Modbus RTU and DH-485.
This feature is specific to the MicroLogix 1100 and 1400 controllers. The other MicroLogix family controllers with this 8-pin port (1000, 1200, 1500) use those pins for +24V DC for peripheral power.
That helps explain it. We've got a lot of experience with the micrologix 1400, where we do use modbus at the rs-232 port. Jeez, it's confusing.
Anyways, I did happen to have a -AIC in the stockroom, so it wasn't a disaster. We do not, however, have a cable, so I'll have to work out what sort of wiring it'll require, still.
I had some recent issues with the analog inputs on an L23E. At first, I did not wire the analog com back to 24 neg and that was a lot of it...
34
3,919
Hello everyone, Anyone know how to factory reset CompactLogix L23E?
1,747
Hello,i need your help. I cant connect to a CompactLogix L23E, I tried via Ethernet and Serial too. The PLC has a IP configured, I have ping it...
1,496
Hello everyone, we want to change IP address for used compactlogix L23E-QB1B controller ,it assigned a IP address before, but this IP address is...
2,811
I am newcomer here, I bought a AB compactlogix l23e embedded i/o plc(used one) a few days ago. I made a stupid decision i think that I downgrade...
1,665