CompactLogix L32E - 1769-IF8 problems

i can't really see what you are doing with it in the logic because your picture is too small. it looks like your EU range should be 3200 to 2100 according to attached chart.

range.JPG
 
CONNECTION: This value identifies the Connection type that exists between the parent and the module. OUTPUT: means Input, Output, and Configuration data types and tags are generated. This just means
that Local:4:O data will also be generated as well as Local:4:C and
Local:4:I data. These three types of data should appear in your
controller tags. This is not your problem. If you have no changing
signal output at your pressure transmitter, that is your problem.
Test your 4_20Ma output at the transmitter, if OK then - you should
see analog input data changing at +Local:4:I.ChOData in your Controller
Tags in your project tree, reguardless of programming.
 

Similar Topics

While trying to download produced and consumed tags with a new controller on the same network I get this error: The maximum number of nodes on...
Replies
8
Views
4,269
hello guys>> i have cpu compactlogix 1769-l32e and i have a program on my flash memory with extension p5k with version 17.004 (17.4)...
Replies
8
Views
2,408
Hi everybody: Is it possible to program the compactlogix 1769-L32E LOGIX 5332E v20 processor with this software? thanks
Replies
2
Views
5,288
OS: Windows 7 Logix5000: 19.01 I have a CompactLogix L32E controller with associated I/O at work that I use to test various programming...
Replies
10
Views
3,996
hey guys I've been having an issue with my HMI not communicating with the PLC. The PLC is a CompactLogix L32E and It happens at random times...
Replies
2
Views
1,128
Back
Top Bottom