CompactLogix Losing Program
jthornton
Jul 2002
Poplar Bluff, MO
295
I have a machine with a CompactLogix 32e processor and it loses the program if you turn it off for a minute. I thought it was supposed to keep the program in memory for a week or so without the battery? Waiting on a battery to show up now but curious if there is anything I can check on the processor?
JT
Those CompactLogix are very similar to the older ControlLogix; they have no capacitor or nonvolatile Flash memory to hold up the program in the absence of the battery.
The SLC-500 controllers could use their capacitor to hold memory for weeks (or months !) and the modern CompactLogix and ControlLogix write their memory to an onboard Flash device at power-down.
I could write a detailed explanation (or link to the RA Knowledgebase) but the simple answer is that a 1769-L32E or -L35E will lose its program immediately if it is powered down without a good battery installed.
same issue with the the 5069-L4200ERMW plc !
is this weird ?
really we need some ups and battery ?!
Yes, you need a UPS. See publication 5069-UM002C-EN-P:
5069-UM002C-EN-P said:
Unlike other Logix 5000 controllers, the CompactLogix 5480 controllers do not have an internal ESM. Instead, you must connect an external uninterruptible power supply (UPS) to the controller to save the state of project if MOD power is lost.
Hello, I got called in last night on a machine that has a CompactLogix L30ER running that suddenly went into "Recoverable FAult" with the OK...
2,288
This has happened several times over the last month. The L18, which is on a UPS, will lose its program and become unresponsive (all LEDs are off...
20
7,594
Good Morning , I'm developing a Shift Register Program for a conveyor system. I begin the Shift Register on a conveyor that is roughly 128...
3,627
Hi everybody, I have an issue with the realtime clock on the AB 1769-L16ER-1BB1B. Every time I cycle the power the time reverts to Jan 1, 1998 at...
17
6,024
Dear All, I have a brand new comapactlogix with an internal build-in ethernet connection. I can give it an IP address. It works fine till i...
2,491