I'm working on troubleshooting a PLC for a piece of manufacturing equipment. The issue I'm trying to resolve is an open wire fault not getting communicated back to the PLC.
The system is running an Allen Bradley 1768 CompactLogix PLC that connects via ethernet to a 1734-AENT adaptor and then to a 1734-OE2C analog output card. This card controls a field device (a control valve). Everything appears to be wired correctly. However, when an open wire fault occurs (i.e. the wiring between the field device and the card is disconnected), no fault information gets communicated back to the PLC itself.
The output card (the OE2C) is reading the fault and begins flashing red for the channel disconnected. However, the adaptor does not show any fault information. When I use a GSV block in RSLogix 5000, the status value that is returned for the channel is 16#4201, which to the best of my knowledge indicates that the card/channel are operating normally without any errors.
Has anyone run into this issue before? Is there a setting somewhere in the configuration that needs to be adjusted to read the fault? Or is there some other issue?
The system is running an Allen Bradley 1768 CompactLogix PLC that connects via ethernet to a 1734-AENT adaptor and then to a 1734-OE2C analog output card. This card controls a field device (a control valve). Everything appears to be wired correctly. However, when an open wire fault occurs (i.e. the wiring between the field device and the card is disconnected), no fault information gets communicated back to the PLC itself.
The output card (the OE2C) is reading the fault and begins flashing red for the channel disconnected. However, the adaptor does not show any fault information. When I use a GSV block in RSLogix 5000, the status value that is returned for the channel is 16#4201, which to the best of my knowledge indicates that the card/channel are operating normally without any errors.
Has anyone run into this issue before? Is there a setting somewhere in the configuration that needs to be adjusted to read the fault? Or is there some other issue?