Hi Guys,

Do the Compactlogix processors have something similar to the Time Base S:4/14 etc. bits that you get in a Micrologix. I quite often use these for flashing lamps etc.

I've searched through the manual but can't see anything obvious.

Many thanks,

Mark.
 
Create a new task. Make it periodic. If you want a 1 second flasher make its period 500ms. In it make a program, in that make a routine. The routine will contain 1 rung. If NOT flash bit - OTE flash bit.
 
The periodic task that Bernie recommends is best as it takes advantage of the superior capabilities of the CLX platform. Learning to properly use tasks will improve your control and your programs.

If you are trying to maintain some semblance of compatibility with an existing ML program and you really do need a free running clock like the ML S:4 then it is simple enough to make one. Create an unconditional timer and call it S4 or whatever name suits you with a preset of 214783647 and unconditionally unlatch S4.acc.30.

S4.acc.30
---------+TON-------------+-(EN}---------(U)--
|Timer S4 +-(DN) *
|Preset 214783647|
|Accum 0|
+----------------+


*you can put output instructions in series in a CLX

Unlatching S4.acc.30 will guarantee that the timer will never time out.
S4.acc.0 has a period of 2mS
S4.acc.1 has a period of 4ms
S4.acc.2 has a period of 8mS
.
.
S4.acc.8 has a period of .512S
S4.acc.9 has a period of 1.024S
etc.

You will have available S4.acc.0 through S4.acc.29. You can assign an alias to any bit in S4.acc. For example, Rapid_Flash might alias S4.acc.8 and Slow_Flash might alias S4.acc.10
 
Last edited:

Similar Topics

Hello I am working with a 5069-L320ERMS2 Compact Guard Logix. I am replacing an obsolete Cognex camera with a newer model. Communication is...
Replies
6
Views
1,799
Does anyone know where I can find a table of the CIP Class/Instance/Attribute values for the CompactLogix system settings? Specifically, when...
Replies
2
Views
4,978
Working on a new Compactlogix system. It has a Prosoft profibus card some analog and digital 120vac I/O And a vhsc card. Had everything working on...
Replies
8
Views
2,203
Im wonderring if the is a system variable or its possible in an other way to get information in to the PLC code about the backup battery on the...
Replies
3
Views
3,936
Hi I just got a new logix5561 from Rockwell. I already had a compactlogixL43 connecting with Kinetix 6000 Servo Drive. The problem is that there...
Replies
8
Views
4,076
Back
Top Bottom