Compactogix IO as RIO for Controllogix
asterof
May 2007
Califonia
554
System 1
1769-L35E with built in Ethernet Port
15 IO Modules
System 2
1756-L73 Controllogix
1756-EN2TR
I want to remove the 1769-L35E and use the compact logic IO
as Ethernet Remote IO on the Controllogix System
Is it posible and how would you do it.
It is possible, but I would leave the L35e in the CompactLogix rack to be master over the IO but slave of the ControlLogix.
I'm sure that you could find sample information in the ControlLogix manual how to perform this.
Jack
System 1
15 IO Modules
System 2
1756-EN2TR
I am afraid this is not possible.
Theoretically, you will need a "1769 EtherNet/IP communications Module" to serve as the 1769 I/O "Adapter"; it might be in the "works", however, as we "speak", the only way to control 1769 hardware is via 1769-CompactLogix CPU and 1769 Backplane.
So your 1769-L35E will have to stay and serve as the EtherNet/IP interface with the 1756-EN2TR subnet.
Once the L35E and L73 are "connected" and the relevant 1769 I/O modules are part of the L73 project, you could use the L35 Inputs and "listen" to the Outputs within your L73 application.
You will not be able to "own" the L35E Outputs; in order to control the CompactLogix Outputs you will have to Produce a L73 Array Tag, Consume it within the L35E application and ladder logic "relate" the Consumed tag to the 1769 Outputs hardware defined tags.
Hello, i am trying to upgrade from a SLC 500 to a Compaclogix L36-ERM. There is a L72 controllogix that uses MSG intructions to read and write to...
3,543
hello, I have a problem with my AN-X2-AB-DHRIO Prosoft module, I can't connect with the module because I lost a microSD card that has firmware and...
406
We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
433
Does anyone have information or documentation regarding the protocol used in Rockwell's Remote IO, and how the physical layer of the network...
948
I have never understood how the I/O is configured using RIO. In the tree there is only the RIO module, not the racks of I/O attached or all the...