Hi,

I has one old Siemens PLC, it is CPU313C (6ES7313-5BE01-0AB0) with only MPI on it. I need to use WWDAserver to read data from it. Two questions:

(1) How could I connect CPU313C to Ethernet/IP network?
(2) Is CPU313C expandable? Can I add ethernet card beside the module?

Thanks first!
 
If you have the space available in the CPU rack you could add an Ethernet CP Lean module 6GK7 343-1CX10-0XE0.
Another alternative would be to update the CPU to a 314C2-PN/DP which has a built in (faster) Ethernet/profinet port.
 
Mike_RH,

Thanks for your quick answer.

Two more questions:

(1) How much difference between CPU313C and 314C2-PN/DP?
(2) Could I copy all the code from CPU313C to 314C2-PN/DP without problem?
 
Cam,
What version of Step 7 do you have?
You have to have v5.5 to use the 314pn/dp, so if you don't the CP module might be easier / less expensive.
For the differences between the two, check the Siemens support site.

Jesper, the OP indicated he would be using WW DAserver to communicate.
 
Thanks again for the answers:

Yes I am going to use WW S7SIMATIC DAServer to talk with CP module,
I am not sure it works or not:

From WW manual:

For S7SIMATIC DAServer from WW, the following protocol are supported:

• TCP/IP with RFC1006
• H1 Industrial Ethernet
• PROFIBUS
• MPI

I have more questions?

What does RFC1006(TCP/IP with RFC1006) mean?
What does H1 (H1 Industrial Ethernet) mean?
ProfiNet means TCP/IP or H1?
CP module should connect to Profinet, right?

Thx
 
RFC1006 is the protocol all S7 PLC uses.
H1 industrial ethernet is an obsolete term from the S5 PLC.
You will be using Ethernet TCP/IP with the WW Daserver, not Profinet.
Profinet is an extension to regular ethernet.

In short, a CP343-1 LEAN module will work fine for you.
Replacing the 313C for a 314C-2PNDP will also work.
314C-2PNDP is much newer and much more performant than the old 313C. Also the integrated PN port is much faster than the add-on 343-1 LEAN module.
The 314C-2PNDP is 4 times as expensive as a 343-1 LEAN.
 

Similar Topics

Hi I am start in vb.net. I want connect PLC S7 300 by Libnodave via USB MPI Adapter for read Input and Output. I searched the internet I found...
Replies
2
Views
3,732
Dear Experts. I have one project using HMI Ktp 1500 comfort and S7-300 CPU 315-2DP. The HMI KTP is using Software TIA porttal for programming, and...
Replies
2
Views
2,044
Hello, I'm not a Siemens person so I'm a little confused what can be missing in siemens ethernet configuration. I have S7-300 with 343 module and...
Replies
9
Views
3,527
I have a Panelview C300 a Micro 830 PLC and also the Connected Components Workbench Even though the CCW seems like it was made to create a...
Replies
9
Views
4,765
hi dear in E300 PROG/SETUP is deasabled by command line. now how can i enable it again?also is any setting to connect a new E300 to FX?
Replies
0
Views
1,499
Back
Top Bottom