Siemens S7-300 can connect directly but not through switch
ryrzu
Feb 2013
Gdańsk
24
Hello,
I'm not a Siemens person so I'm a little confused what can be missing in siemens ethernet configuration.
I have S7-300 with 343 module and i want it to communicate with KepServer (which is on another subnet).
Right now i tested connection by connecting directly S7-300 and my laptop's virtual machine kepserver and it worked but when i connected it through switch (without changing ip addres of my laptop) i couldnt connect to it. I was still able to ping it. What should i check? what can be missing in Siemens configuration? If i can ping it (even in different subnet) it seems that ip and gateway is set correctly...
IT department of course say there is something wrong with siemens configuration but i believe it can be something with switch. I need to prove that it's not siemens configuration related. Please help me.
You say you're trying to do routing. Is there any NAT involved, or is it straight layer 3 switching? Is there a firewall involved? Port 102 must be open.
If the IP address, subnet mask, and gateway are set correctly on the cp343 you are plugged into, then I don't think there is much else to worry about configuration-wise.
Also.. If I am not mistaken, if you are using a profinet connection for some reason, this will not work if you are routing. It should work with a switch.
Does not seem to apply for your case, but thought I would throw that in.
Boneless makes a good point. Profinet IO communication is layer 2 (MAC address and device name) not Layer 3 (IP address), and therefore does not support routing. This makes for less overhead and faster communication, and I've never heard of a case where it was a good idea to route IO from one network to a PLC in another.
However, an OPC server connection uses ISO over TCP, which is layer 3, and does support routing.
Guys,
It's getting weird. I can telnet to siemens on port 102. I can ping it. IT said they disabled all security on siemens port and my laptop port (on switch). Still I'm not able to read tags...
@rdrast - yes it's managed switch i'll try with not managed
@mk42 - we tested it with all security between used ports disabled - still no go
@boneless - thanks for heads up! but as mk42 stated OPc server use tcp so it's should be easly routable
I conntacted Kepware support but after answering their questions they say it's network related and they can't help me much.
Hi All, I have siemens CPU-300 with DP port. which i am using as master for DP slave. Now i had some SLC IO which i want to connect to the same...
4,787
114
Hello all. I have an ESA HMI that is connected to a Simatic S7-300 (CPU312). I have uploaded the program from the PLC which is written with Step7...
1,467
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
703
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
1,080