Connection issues to my Siemens CPU

orense

Member
Join Date
Apr 2006
Location
Norway
Posts
196
Hi,

I have a plant where we recently changed CPUs from 315-2DP to 315 -2PN/DP.
They are all connected to a Beijer panel. Strange thing is that one of them I can only connect to with my laptop and Simatic Manager when I disconnect the panel. If the panel is connected to the switch where all the CPUs are connected, this one CPU is completely impossible to connect to over Ethernet.

Does anyone know what this might be? Can the CPU ethernet interface be loaded so heavy against the panel that it cannot connect to anything else, or is it maybe some setting which is incorrect. I have worked many years with Siemens Plcs, but I have never seen this before.


A
 
Thank you for replies.

I figured it out.
I had to increase the PG number setting under communication tab in the CPU properties.
Default value is 1, but it seems that the panel I am using is occupying this connection as a PG. Therefore I had to increase value to 2, and I was able to also connect my laptop as a PG and monitor the CPU at the same time as the panel was running connected.
 

Similar Topics

I am working on a project to back up software for a number of machines for a client, and am having problems connecting to SIMOVERT MasterDrives...
Replies
12
Views
3,152
Hi folks, I'm having trouble connecting to a Siemens Simatic S7-300 CPU 315-2PN/DP via ethernet from a PC using Hyperterminal, I have the correct...
Replies
28
Views
21,934
Looking for some help with the connection issue between Citect 2018 and Top Server v6 for Opto22. I’m setting all this up to communicate with some...
Replies
0
Views
121
I am working with a 1768-ENBT and I was able to connect to it through my laptop. My laptop IP is 192.168.1.10 subnet 255.255.255.0 and the PLC...
Replies
12
Views
1,576
I am trying to get to the bottom of a fault for a client and need to get online to a Schneider TSX3721001. I am able to get the unitelway driver...
Replies
11
Views
2,496
Back
Top Bottom