I've experienced a very unusual problem and searching I came across this forum and thought I'd give it a shot.
I am not a PLC specialist, my business is industrial ethernet networks. The problem came up at a particular plant where I was replacing a 3com office line (superstack) switch with a Hirschmann MICE industrial switch.
Basically it is a very small network, consisting of 4 PLCs (2x Control Logix + 2x SLC) and 3 workstations. What is usually a very smooth changeover had a serious glitch today - one of the PLCs could not be PINGed or picked up by RSLinx. The weird thing is that the SNMP software for the Hirschmann switch was showing the correct MAC address connected to the port on the switch, and the activity light was on, so there definitely IS a connection. After fiddling with the speed and duplex settings, and nothing having any effect, I did the following: plugged the offending PLC to the 3com switch, and then the 3com switch into the Hirschmann switch - now I could ping it, RSLinx could see it and everything was OK.
Then, I got the PLC guy to prepare a new ENET module with the particular IP address, to eliminate any problems with the module. He did, and as he plugged it into the backplane, same situation - I could see its MAC on the port on the Hirschmann switch, activity light was on, BUT this time I could PING it!!! Unfortunately, still no joy with the RSLinx.
I had to leave with the sad state of affairs, having plugged the PLC into the 3com and then the 3com into the Hirschmann switch - thus negating the purpose of the whole changeover.
I have done this numerous times with exact same PLCs and never had this problem. The other PLC on the same network was instantly recgonised and picked up by RSLinx. I compared the settings of the two ENET modules and there was no difference (apart from the IP addresses of course).
I am really baffled, can someone help or point me to a resource where I could read up on what may be causing this?
Thanks,
Vlad.
Can be an anomoly in Linx. Delete the linx driver, shut down linx, restart linx and reconfigure the driver. good chance it will all re-appear. Regards Alan Case
If you can PING a new module - your hardware is OK.
Most likely it is RSLINX issue.
Is firmware revision of the new module is the same as old?
If not your RSLINX may need EDS file.
Is your new module ENET or ENBT?
For ENBT you will definately need EDS.
Do you have any other communication going over this module (Produced/consumed, message, HMI)?
As I said, I could ping the new module for a while and then it just stopped responding. I would also suspect a fault in Linx if it wasn't for the fact that Linx picks it up straight away (and I can ping it) when I use the 3com switch..
Cant offer any help but I had the same thing happen when I tried to connect to a CLX with a Linksys switch. Swapped out the Linksys for a 3Comm switch and it worked fine. Dont have any idea why the CLX did not like the Linksys switch. System has been running for about 3 years now with 3Comm switches and have had no problems.
I am having problems trying to get either the SMS or Email to work. I have read every post on here and else where and do not have a tech connect...
3,267
Hello, I have a new CLX, I powered it up downloaded the firmware, configured the I/O's, but I have two cards left a Enet and a DHRIO Anyone...
4,849
Hello all, I'm looking for some help with my DeviceNet. I have a 1756-DNB scanner in a rack with a Control Logix 5561 processor and my network...
6,242
I am trying to setup an RMC100 motion controller to communicate via EthernetIP with a control logix processor. I have followed the instructions...
7,621
251