Control Logix Programmable Limit Switch

robertmee

Lifetime Supporting Member
Join Date
Feb 2008
Location
NC
Posts
2,038
Anyone here use the 1756-PLS or the AMCI 8213?

Have a customer that wants to replace an old autotech that stitches glue. The on/off cycle is 32ms on, 16ms off, with 1ms equating to .04 inches, which is near the tolerance of positioning. So anything that requires a 2ms update time in CLX is out, which due to RPI's means no HSC card coupled with output modules. I know the HSC has a couple of outputs that can be tied to position windows and turn on outside of PLC scan, but it's limited to two windows and I need at least 4 or more for the patterning.

The customer doesn't want to use another standalone PLS, but wants it integrated into an existing L71 ver 20 PLC. Hence why I'm looking at the two solutions above. I'm open to any other suggestions or anyone's thoughts that has had experience with either module.
 
I used AMCI products with SLC and PLC-5 controllers and they were outstanding. Easy to program (even with block transfers), reliable, straightforward documentation. I suspect they will be even easier to use with the Logix 5K platform.

I used their HT-20 resolvers with modules that had no outputs as well as one machine that did have built in outputs on the PLC-5 module and they did what the mfg. said they would do. With more than a hundred of them in use for many years, we never had a resolver fail, only a few broken connectors over the years. When you climb all over a machine and use the cables like a rope ladder, that is to be expected.
 
Last edited:

Similar Topics

I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic...
Replies
11
Views
271
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
Replies
2
Views
388
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
Replies
8
Views
782
Possible for two processors in same rack to have separate motion groups across a single Kinetix Rack using a single EN3TR? One 6500/5700 rack, 8...
Replies
1
Views
435
Hi all! I am hoping to find some help understanding the ABB VFD Connection to my Rockwell PLC. I have set up the VFD parameters based on...
Replies
4
Views
693
Back
Top Bottom