Control logix with Panelview plus communication
sandy5020
May 2012
vadodara
112
We have around 10 PV Plus HMI connected to CLX via ethernet IP-CAT6 cable it was working in good condition for few years but now there is some communication issues ie all of the HMI communication may freeze for around 1-2mins this is very critical for production...any one have a solution?...
Regards
Sandy
Are they all connected to a common network switch? Is the switch managed? Some switches will take about 2 minutes to start forwarding packets if they reboot. Can you visually look at the indicators on the switch to see if all the lights go off when the fault occurs?
If it's critical for production, then you should assign some assets and efforts to it. That includes spending time examining and documenting the network architecture and the diagnostic capabilities of every element.
It should be self-evident that there is not a "do not malfunction after a decade in service" checkbox in the ControlLogix or PanelView Plus software.
The questions I recommend starting with are:
Describe the exact symptoms of a "data freeze" event.
Do all ten of the PV+ units undergo this failure at the same time ?
Are there network elements like switches or uplink cables that could be responsible for the failures ?
What error messages do the PV+ terminals show in their FactoryTalk Diagnostic histories ? It may be useful to set all the PV+ terminal clocks to the correct local time so that such histories can be compared.
How long is communications interrupted, or the "data frozen" ?
Do any other network communications interruptions on the networks that include the PV+ terminals occur, such as I/O faults or inter-controller data exchanges ?
The ControlLogix ethernet modules have some very useful information about uptime, connections, and CPU utilization built into their diagnostic webpages. It may be helpful to examine or record this information periodically, especially in the immediate aftermath of a "data freeze" event.
I have had similar situations in the past, 9/10, someone ran High Voltage in parallel to communication cables.
Also check to make sure you are not fighting for Connections inside the PLC.
Have you looked at the diagnostics in RSLinx?
Wireshark?
Hello all, I know I have asked questions on this before, but does anyone have insight as to why discrete I/O would work on some screens but not...
1,596
All, This is my first time test and attempting to establish a DHRIO connection in my career, I am attempting to upgrade the main processor in the...
1,401
So I've been getting around something that is confusing me. Attached are my notes. I have a tag that I can change in an Panelview32. I found...
3,499
I am new to this and gotten my hands on the follow device for learning. Was told it was fully functional, but have ended up finding it not to be...
17
6,517
Hi, newbie here [you have been warned :) ] I have a basic application using RSLogix 5000 [v20] and FactoryTalk View ME 6.10. I have imported the...
1,451