ControlLogix 1757-SRM problem
ashley
Jun 2002
Perth
58
Hi, we have a problem with a 1757-SRM module (ControlLogix System Redundancy module) used in one our projects. The OK LED on the SRM is solid red and the power up self test gets stuck on TH73. Has anyone come across anything like this. Could you advise what is the problem and its possible solution.
Appreciate your help.
I haven't seen it. But I do have some questions and suggestions.
First, check Allen-Bradley's literature. There will be a page that explains what the LED signals mean. Sometimes this helps.
And here are some things we may need to know to help you:
1) Do you have the fiber cable on the SRM module connected to another SRM module?
2) What cards do you have in the PLC racks? Are they in the same slot in each?
3) Have you installed the same version of the firmware in each SRM module, processor, and i/o card?
4) What version of the firmware & software are you using?
AK
Thanks for the replies.
akreel,
Allen-Bradley's literature doesn't mention anything about the startup tests for the SRM module. There is no manual for the SRM module. Only installation instructions. The installation instructions booklet does give information about the error codes but nothing about the startup self test codes.
Regarding your questions,
1) The fiber cable is connected to the two SRM modules
2) The cards in the various slots are as follows:
Slot 1: 1756-CNBR Ver. 5.36
Slot 2: 1756-CNBR Ver. 5.36
Slot 3: 1756-L55M13 Ver. 11.6
Slot 4,5: Empty
Slot 6,7: 1757-SRM Ver. 3.25
3) I have installed the same version of firmware in each SRM, processor and CNBR
4) Software version 11.11
The system was working fine after commissioning. One fine day the maintenance guy calls up and tells me that the redundancy is not OK.
On first observation, the LED display on the SRM was blank and the OK LED was solid red.
So I cycled power to the secondary chassis. This is when the SRM module didn't go past startup self test TH73 and I also get the following message on the CNBRs:
ASSERT: wait4sbm.c line 0114
I had the same Problem with the SRM Module, I tried the below steps and found that the fault(TH73) was recovered.
1. Remove the SRM Module from the Chassis.
2. Unscrew the Module Cover and remove the PCB set.
3. Dismantle both the PCB's from each other.
4. Remove the dust particles from the PCB's using the Blower.
5. Keep the PCB's asside for around 10 Minutes.
6. ReConnect the PCB's and place it back inside the Slot Cover.
7. Install the SRM Module inside the Chasis and Switch it ON.
8. Hope it will work.
If not, repeat the above steps 2 to 3 times.
Thanks.
Salin Jayasankar
We have a problem with a 1757-SRM module used in one of our projects. The OK LED on the SRM is solid red and the power up self test gets stuck on...
6,076
TonyBabu
T
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
86
Hello, I have two 16 point input cards and 1 16 point output card showing module faulted on my IO tree in Logix Designer. The fault code is...
216
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
198
Trying to setup a message read via Ethernet. I have the path setup as 1, 1, 2, 192.168.66.10 I get an error code 1, ext err 315. I am beating...
233