I can't access the links at work, but is the counter 10000, and the accumulation is over 300000? I find that odd. Not impossible, just odd.
A proper reset of the accumulator would reset FIT_017_COUNTER with a (RES) instruction, which would then cause FIT_017.TOTALSTORE to drop to zero.
Bradal,
Lets stop dancing around. Can you please post the program? If not the program then at least the entire subroutine and UDT structure. These videos give us nothing more than a peek through a key hole and display only the symptom and offer absolutely nothing whatsoever of use in determining the cause.
CTU instruction but if you need to count up higher than 32,767 (for instance on a high speed bottling line that does 10,000 pieces per HOUR), then you need to use a floating point value.