ControlLogix hotstandby redundancy
abaig
Jan 2007
Pakistan
17
Dear All,
I want to know that in controlLogix hot standby redundancy configuration what will be the ethernet addresses of my enet cards.
Will they be same or different.
If they are same will it not conflict on the network
and if they are different then how will the other PLC communicating with this redundant PLC system switch to communicate on different ethernet addresse.
thanks and best regards
Hello abaig;
From the Controllogix redundancy manual:
Hope this helps,
Daniel Chartier
Make sure you are using appropriate versions of Logix and firmware - for example Version 16 with the recommended firmware pack. You will assign two IP addresses in series. The SRM modules will switch the IP address of the two Ethernet modules depending which rack is primary. The primary rack will take the lower IP address. Each IP address will respond to pings and http.
Earlier versions of Logix/Firmware had issues. I just tested a system using Version 16 and all appears to be working well.
Just wondering how you tested ver 16 redundancy if it will not be out for at least another 6 months?
The current redundancy is ver 15.
IP swap works without any problems with ver 13 and 15 of redundancy
Right! Contr.
I have confirmed with AB that v16 does not support redundancy right now however this feature will be provided later this year.
103
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
105
Hello, I have two 16 point input cards and 1 16 point output card showing module faulted on my IO tree in Logix Designer. The fault code is...
234
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
223
Trying to setup a message read via Ethernet. I have the path setup as 1, 1, 2, 192.168.66.10 I get an error code 1, ext err 315. I am beating...
255