Trying to setup a message read via Ethernet.
I have the path setup as 1, 1, 2, 192.168.66.10
I get an error code 1, ext err 315.
I am beating my head against the wall trying to figure out what's going on
in an offline project, add the controller to the i/o tree then in MSG config dialog, pick the path from the i/o tree item. then delete the i/o tree item, and the path remains.
That's a CIP connection error, to be sure. But I don't think that CIP paths are so complex that you need to fake out Logix 5000.
That is correct for a 1756-ENxT module in Slot 01 (the second slot from the left) and a PLC-5E at that IP address.
>PLC-5/80E ver D.1
The Series letter will matter. If it's a PLC-5/80E Series E, Version D.1 then that's the first version that supported CIP protocol and can accept a message from a ControlLogix. Are you using the PLC-5 Typed Read or PLC-5 Typed Write command ?
Using the Windows PowerShell "tnc" command to check if the PLC-5 supports CIP would be my test.
Verify the PLC-5's embedded webserver on Port 80
tnc 192.168.66.10 -p 80
Verify the old PLC-5 CSPv4 protocol on Port 2222
tnc 192.168.66.10 -p 2222
Verify the modern CIP protocol on Port 44818
tnc 192.168.66.10 -p 44818
An example of what a successful tnc looks like, for a 1756-ENBT in my lab:
Code:
Windows PowerShell
Copyright (C) Microsoft Corporation. All rights reserved.
PS C:\Users\kroach> tnc 192.168.18.228 -p 44818
ComputerName     : 192.168.18.228
RemoteAddress    : 192.168.18.228
RemotePort       : 44818
InterfaceAlias   : Ethernet
SourceAddress    : 192.168.18.104
TcpTestSucceeded : True
If you have support contract then you can read Technote QA2752 | Access Levels: TechConnect.
This specific error is related to the incorrect message path, but also linked to the manipulation MSG block bits, specifically for PLC5.
I would create a completely new tag first, then deleting old tag. Also remember that message executes only once when rung condition changes from False to True. Use NO contac and toggle it for a test.
That fixed it. Not sure how I missed that in the KB ...
I'm having an issue trying to backup a ControlNet network. Within RSLogix5000, when I click on Module Properties of the 1756-CNB (Rev 5.001), the...
907
I have followed several videos and tutorials that suggest when using the MSG function to enter 2,xxx.xxx.xxx in the Path box in order to connect...
1,434
Hi, I usually work with siemens and the TIA portal but a customer has a series of cabinets I do with Micrologix and Panelview Plus 6, I haven't...
2,255
First question, is there any easy way to convert the symax logic onto the controllogix? I believe we have an old laptop that will connect to the...
2,349
Is is possible to create a message string within the L71 controller to send as an email through the 1756-EWEB Module?
1,209