ControlLogix Major Fault Code 23

wa5yom

Member
Join Date
Sep 2003
Location
Ardmore, Oklahoma
Posts
138
I have a ControlLogix configured with 2 PanelView Plus 6's two individual DLR networks.

1 DLR Network has 5 Armorstart drives.

The other DLR Network is a combination of Point IO and Armorpoint IO.

There is also some local IO.

Upon a cold start (turning on the main disconnect), the processor always has a major fault.

Fault Code 23, "At least one required connection was not established before going into run mode."

This is not intermittent.

Upon clearing the fault....everything works fine.

Any ideas?

Thanks,
Tim
 
Last edited:
One of your modules has the following boxed checked in the connection tab:
"Major Fault On Controller If Connection Faults While In Run Mode"

Most modules will cause this on a power up.

You could write a fault handler routine to check for and clear this specific fault on Power Up ONLY that way you would still get the fault later on if required.

Unless you want the controller to fault when a module has a comm fault to the controller, then always uncheck this box.
 

Similar Topics

Hello, We have a customer with a 1756-L72 ControlLogix PLC. They have recently got a T01:C62 Fault Code. I am trying to figure out how to...
Replies
6
Views
1,050
:scratch: I have a strange behavior, sometimes Major Fault Type 4 Code 20 occur, I know the reason, I used an array with a word index which can...
Replies
23
Views
9,003
Hi Experts, I need to test if a ControlLogix redundancy system will switchover when the Primary chassis has a major fault occurred. I followed...
Replies
2
Views
1,849
i need to obtein type and cod by fault in a controllogix i am try to use at gsv instructions but i can´t any informations could some one help me
Replies
3
Views
4,492
Hello, My Controllogix PLC stops with a major fault after cycling of power. Why?
Replies
4
Views
4,826
Back
Top Bottom