ControlLogix - Modbus TCP & EtherNet/IP
rngtech
Jul 2022
London, England
Hello all,
I was wondering if you clever people could help me, please.
In the past I have used a standalone L33ER CompactLogix PLC with the Modbus TCP AOI to talk to another Modbus TCP device. I know its not as good as a standalone Prosoft etc, but seemed to work fine (the customer does not like using other modules/gateways).
The site I am working on now has a ControlLogix rack with a Logix5572 with EtherNet/IP Module. The Ethernet module connects to a Hirschmann switch which has a HMI and a MicroLogix PLC.
Am I able to connect my new Modbus TCP system to the switch, implement the Modbus TCP AOI to the PLC and then allow these 2 Modbus systems to communicate, as well as maintaining the original connection between from the Logix5572 and the HMI/MicroLogix PLC? If this is possible, is it only with the 1756-EN2T Ethernet/IP Module, and not the 1756-ENBT.
Thank you!
Yes. Any Ethernet switch will carry both the EtherNet/IP traffic as well as the Modbus TCP traffic (along with any other Ethernet protocol).
Should be fine. Also, if that MicroLogix is a 1400 Series B/C, it can communicate via Modbus TCP natively.
1756-ENBT does not support sockets. EN2T does.
Also this Ethernet module must be in the same chassis as controller.
Otherwise, what you described should be Ok.
I am working on a project, inside an AB CLX, I implemented the Modbus TCP Client AOI published on AB website, to interreact with a Modbus ASCII...
3,584
I am not very experienced in Rockwell PLCs and have run into a small problem, so I could do with a little bit of help. We have a redundant...
2,534
Hello All, I'm looking for the Coles notes on how to inferface a Modbus TCP device (compressor controller) with a Logix 1756 L72 running V24...
5,890
Hi all, I'm working on a wastewater plant where I have a ControlLogix PLC as the master PLC, alongside three packaged systems that are being...
3,867
Hi, Do you guys know of any marine (ABS or DNV) approved modbus TCP solution for Rockwell Controllogix? Our system: Redundant 1756-L72 - Act as...
2,066