Normally I would use
1756-L61, 1756-CNB2, 1756-ENBT, 1756-RM
for a ControlLogix Redundancy System

However the customer does not want ControlNet
and wants Ethernet IO, but wants the IO separately from the
HMI Lan. Any Ideas on how to do this not using a backup channel on the HMI OPC
 
If I understand your needs, it sounds like you just need an Ethernet I/O network and another Ethernet HMI Network.

Your HMI will simply have a shortcut that points to the IP of the Primary chassis. On failover the IP's swap and your HMI is now connected to the other chassis. You will have to have 2 Ethernet cards in each chassis.

I think you have to use EN2T's though. Verify in the manual.

I do not see an issue, or I do not understand the question.

RSL
 

Similar Topics

Hi, Good day to all, I got a situation regarding the redundancy configuration. Please refer to the image attached (Page 26, Enhanced...
Replies
17
Views
9,667
We're just looking at setting up a redundant ControlLogix chassis pair. The pair communicate to a single I/O rack via Ethernet/IP, and we will...
Replies
6
Views
3,371
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
Replies
1
Views
103
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
Replies
4
Views
214
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
Replies
0
Views
94
Back
Top Bottom