I believe that there is an anomaly in the Rockwell 1756-L1 (and others?) v34 controller. As of this writing, controller v34.0 and v34.011 have it.

The symptom is difficulty in getting or staying online with Logix Designer. The problem only appears when a program is loaded. For example, flashing is unaffected. Using either RSLinx Classic or Factory Talk Linx has the same effect.

Using RSLinx, the errors are 806-804535 or 701-804353 depending on whether you were online or not.

The solution is to open the Main Task properties > Configuration tab. Then check the box labeled “Disable automatic output processing…” You should then be able to download the program and stay connected.
 
I don't think so. Bought it from our usual distributet who is pretty huge.
I talked to 3 different departments on the Rockwell support line. The hardware guy is the one that found the solution.
 

Similar Topics

I'm trying to integrate a Beckhoff IPC with a Controllogix PLC. There is some documentation, on the Beckhoff website, on how to do a PLC-PLC comms...
Replies
0
Views
69
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
Replies
1
Views
91
Hello, I have two 16 point input cards and 1 16 point output card showing module faulted on my IO tree in Logix Designer. The fault code is...
Replies
7
Views
224
Hello, My associate and I are trying to sync up two ControlLogix racks (7-slot chassis) with identical modules. We are able to see the secondary...
Replies
4
Views
209
Trying to setup a message read via Ethernet. I have the path setup as 1, 1, 2, 192.168.66.10 I get an error code 1, ext err 315. I am beating...
Replies
9
Views
247
Back
Top Bottom