With only one remote Flex I/O node communicating to a 1756-CNB, will only one segment terminated at both ends work? Or do I have to add an intermediate tap with a dummy load to create two segments?
 
You might be able to get by without a T-Tap + Dummy Load, depending of the trunk coax run length and the eventual scheduling requirements or at least I have seen similar setups running with a 20ms RPIs within non -scheduled topologies.
However, http://literature.rockwellautomation.com/idc/groups/literature/documents/in/cnet-in002_-en-p.pdf Page 2-7 states that 75Ω terminating resisors are a must.
T-Taps and Dummy Loads are pretty inexpensive and you should try using the recommended installation hardware components for future expansion and proper functionality; why would you run the trunk coax directly into the comms adapter other than while within an "emergency"?

Dummy Load 1786-XT $9.93 List
T-Tap 1786-TPS $121.00 List
 
Not sure what you mean by "emergency", but I do intend to connect terminating resistors on each end of the link. I guess the question could be re-stated as...in a non-redundant ControlNet network, what is the minimum number of nodes? 2? or 3?
 
2.
Installing a Dummy Load T-Tap will not create a new segment.
Install as many taps as required nodes.
 
Last edited:
Make sure you aren't confusing the physical T-taps or Y-taps with the logical 'Nodes', which are the actual automation devices.

Understand also that devices with two BNC connectors, like the 1794-ACNR15 adapter, have two separate channels (A and B). The signal doesn't pass from one channel to another in a daisy-chain.

A ControlNet network with one 1756-CNB and one 1794-ACN(R)15 adapter must physically have two Taps, two Terminators, and a trunk cable.
 

Similar Topics

Hi, we need to add some ControlLogix IOs to a remote rack via controlnet, based on the info from Ab, Lodix V15 could do it on line, there are...
Replies
9
Views
3,471
Hello All, I am looking for an option to connect Beckhoff remotes I/Os to control logix L73 processor over ControlNet using Beckhoff coupler...
Replies
0
Views
1,842
Does anyone know if its possible for a Non-Allen Bradley controller to acquire IO data from a module in an Allen Bradley remote rack (lets say a...
Replies
5
Views
2,471
I'm having a brain block here so help me out. For AB 1756 IO connected with ControlNet, what happens during a com lost? Does Analog out goes to...
Replies
1
Views
2,053
Hi, why One projects' remote controlnet Rack Do point is not off while disconnect controlnet cable tap? The 1756-OB16I module's Comm Format is...
Replies
3
Views
1,808
Back
Top Bottom