Lifetime Supporting Member
Hello all,
My current project involves using a panelview 1400 with controlnet. This is my first job using control logix, and do I have lots to learn.
My question is this, I tried without succes to address a multistate indicator to the bit level of an array word {array_1[10].0}. The array is configured as an INT, and I have used whole words in this array for message displays, but haven't been able to use individual bits. Two screens I built have a total of 83 multistate indicators (using just states 0 and 1), and I wanted to use 6 words of a 70 word array, and not 6 words of the 32 configured for the panelview. When I first downloaded to the panelview, these two screens showed error states for every indicator. After changing the addresses using the words configured in the processor for the panelview, everything works fine.
Anyone have a clue?
My current project involves using a panelview 1400 with controlnet. This is my first job using control logix, and do I have lots to learn.
My question is this, I tried without succes to address a multistate indicator to the bit level of an array word {array_1[10].0}. The array is configured as an INT, and I have used whole words in this array for message displays, but haven't been able to use individual bits. Two screens I built have a total of 83 multistate indicators (using just states 0 and 1), and I wanted to use 6 words of a 70 word array, and not 6 words of the 32 configured for the panelview. When I first downloaded to the panelview, these two screens showed error states for every indicator. After changing the addresses using the words configured in the processor for the panelview, everything works fine.