Contrologix IO Tree and HMI Units
The Plc Kid
Feb 2009
Macon, Georgia
3,233
So I am doing a project with 4 10 inch Panelview plus units and 3 17 inch versaview panels. The Panelviews are running ME and the 3 versaviews are running SE.
The panelviews are for specific location 2-3 screen HMI control and the versaview units have the entire machine project about 80 screens.
So I have a few Questions
1.0 I see where the panelview can be added to the IO tree. Should I do this? What is the avantage of adding them? They are working well now without being added.
2.0 Can the versaview units running SE be added? I did not see a way to do so. It would be good just as kind of a documet to what is on the system I think.
The panelviews show up in Linx but the versaview units don't so thats why I was looking for a way to maybe add them to the IO tree.
Both answers are "No", for terminals connected over Ethernet.
The PanelView terminals you see available in the I/O tree are for PanelView Standard terminals, not PV+. Those terminals had an I/O object they could connect to the ControlLogix over EtherNet/IP but the PV+ terminals do not.
When you browse an EtherNet/IP network with RSLinx Classic, what you're seeing on the PV+ terminals is the RSLinx Enterprise EtherNet/IP driver. It responds to Browse functions on the network, so it shows up as an icon.
A FactoryTalk View SE client station probably won't be running RSLinx Enterprise, so it won't show up in an RSLinx Classic browse. An FTView SE Server should show up in a browse, because it is (very likely) running RSLinx Enterprise.
That doesn't really surprise me; maybe there's an Windows firewall thing, or maybe the full RSLinx Enterprise doesn't respond to browses.
Either way, don't put a PanelView Plus in your I/O tree; it won't connect and it might interfere with the ordinary tag reads and writes from the terminal to the controller.
Can anyone confirm that using contrologix 5580 controller is not possible to work with powerflex 527? It's been a couple of days now that i am...
1,196
Hello, I have a flow control PID that keeps locking up. It seems to control fine but after a while the output no longer moves. For instance...
971
Hi everyone, I can't add any modules to the Controllogix backplane and it doesn't matter online or offline. Both is not working. Please see the...
2,992
Hello, I have a question regarding the possibility of using messages instructions to communicate between: PLC5/80E Series D - CE Water Mark...
3,066
I have a customer who wants to control his DCS800 drives via Ethernet, so I have bought two RETA-01 cards. At the moment they are connected via...
1,002