Contrologix PID software manual control
yam785
Jul 2004
pa.
153
I am using a PID instruction to control system speed reference to two drives, based on the end of line machine current load. The requirements are to:
1. Auto Mode-PID output controls speed reference based on machine load%.
2. Manual Mode-Software manual mode holds output, and allows set output to be entered.
3. Back to Auto Mode-PID output starts controlling from the set output entered.
The problem:
I have the panel set-up here in office, doing testing. In Auto, the PID controls as it should when I vary the process variable.
I can put the 'SPEED_CONTROL_PID.SWM' bit in the tag database to a '1', the PID does go into Software manual mode, and allows me to enter a value into 'SPEED_CONTROL_PID.SO' in the tag database. When I put a '0' in 'SPEED_CONTROL_PID.SWM' bit in the tag database, the PID goes back to Auto, and starts controlling from the set output entered in Software Manual Mode.
This is exactly how I need it to work. But when I try to put logic in the ladder file to access these parameters, it won't accept the tag type. I keep getting the error, 'argument does not match instructions.
Wait- what the hell? Now while trying to duplicate the problem, to allow me to explain the problem, it accepted it, and works perfect now.
Thanks for the help anyway. I hope this was at least a good discription of the problem, as I've seen the discussion going on about questions asked.
Thanks.
I don't really understand why you are using intermediate tags such as SPEED_SELECT. If you are performing your control from some sort of HMI, you need to link .SO tag directly to a numerical data entry object. When loop is in auto, it will ignore your entry into this field. But when in manual - it will set loop output based on your input. When switching back to auto - it will pick from last entry.
val_99 said:
Oooh Err !....somebody mention "bumpless transfer" !!
Hello, I have a flow control PID that keeps locking up. It seems to control fine but after a while the output no longer moves. For instance...
968
HI ALL, I am trying to write a program with rslogix 5000 for contrologix is there any other ways to modulate a valve with out using PID blocks...
8,477
What is the safe max amount of pid loops that i can put into a contrologix processor without overloading it? These will all be steam valve...
3,341
What is the difference between the pid and pide instruction? Where and why would i use one as opposed to the other. My equipment has pid...
9,732
What is the best method of temperature controls single loop controlers or pid loops in a plc? What are the primary differences between the pid...
7,879