convert 4-20ma to 0-10v with resistors?
TimD
Aug 2007
New Hampshire
235
Hi, I have a MicroLogix 1100 PLC, and it has two 0-10v analog input channels. Is there a way to convert a 4-20 ma loop powered device for use with this PLC? I thought I could use 250 ohm or perhaps 500, but am unsure.
Thanks!
OK, fair enough! One more question, resistor ACROSS the two input terminals or in series with one of the input leads?
Many Thanks!
Also note that it should be a precision resistor.
The recommended is a 500ohm low-drift precision resistor valued at 0.05% or 10ppm and 1/4 watt.
Personnaly i don't use that high a precision resistor but dont go using a common 5% or 10% one either.
Cheers,
Andrew
Agreed. 1% and 2% can be found on the shelf.
There is 2 factors to consider. Some may think you can just measure actual resistance with a precision meter, but that's not enough.
The tolerance is also over time as the resistor ages. You can help reduce this a little by oversizing. Use a 1 watt resistor, for example. At 20 mA, it will never get much above room temp, so no thermal induced aging. Put shrink tube over it so humidity, etc. doesn't attack it.
Do these things and you can relax a little if 2% is the best you can find.
So in the past I have converted a 4-20ma signal to 0-10v using a 500ohm resistor. I am attempting to control a Johnson Controls damper motor with...
1,617
Hi! I have a Belimo SGF24 which provides a 0-10V (or selectable 2-10V) output. http://www.belimo.ch/pdf/e/2_Z_4_e5.pdf Is there a simple...
18,674
Have a question. Have a transducer that gives a 0-10v output. Is there a way to add a resistor so that it would appear as a 4-20ma signal?
23
54,597
Got a new piece of equipment that has a flow switch on it. But the flow switch is 4-20ma output and we don't have any analog inputs left and the...
19
5,256
Greetings all, In a project I'm working on, we have an 4-20ma temperature transmitter linked to an S7-1200's analog input (0-10V reading 2-10V...
1,759