So I have a system that is running on DeviceNet. We have been having nothing but problems with it for the last 3 years. I am trying to switch one node of Remote I/O from communicating with a 1769-ADN to a 1769-AENTR. I have never had to configure an SM2 before, and I thought I did everything correctly by reading the manuals.

There are 3 local 1769-SM2s and then 2 more in this remote rack. When I readdressed everything i copied the logic from the Local ones and just addressed to the remote ones. When I installed the new AENTR and downloaded the program all of the drives just either give a comm loss fault, or sit there and do nothing.

I have included both versions of the ACD file and the DNT file if someone wants to take a look and see what I did wrong, I would greatly appreciate it.

Files too big to attach. Can be found here..
https://drive.google.com/drive/folders/1E3Pjfx_Hhq3_e011iFle9TSxwYpTWgYX?usp=sharing
 
Last edited:
It's one of the rare things that the DeviceNet software does better than Studio 5000... the configuration module profile for the 1769-SM2.

In your DNet configuration, it shows the three channels on each module configured for different numbers of slave drives:

Slot 1 Port 1: Drives 0-4
Slot 1 Port 2: Drives 0-4
Slot 1 Port 3: Drives 0-3

Slot 6 Port 1: Drives 0-3
Slot 6 Port 2: Drive 0
Slot 6 Port 3: Drive 0


In Studio 5000, there is no module profile that shows you the meaning of each Configuration word. So we have to go back to the user manuals and the example code, or copy the configuration values from similar modules as you did.

My reading is the Configuration element that describes the number of drives per port (DSI I/O Config) are elements [3], [17] and [31].

Let's compare them for all the 1769-SM2 modules in your system:

Local:4:C.Data[3] = 0x0004
Local:4:C.Data[17] =0x0004
Local:4:C.Data[31] =0x0000

Local:5:C.Data[3] = 0x0003
Local:5:C.Data[17] =0x0004
Local:5:C.Data[31] =0x0000

Local:6:C.Data[3] = 0x0003
Local:6:C.Data[17] =0x0003
Local:6:C.Data[31] =0x0004

Corrugation_RIO:1:C.Data[3] = 0x0004
Corrugation_RIO:1:C.Data[17] = 0x0004
Corrugation_RIO:1:C.Data[31] = 0x0000

Corrugation_RIO:1:C.Data[3] = 0x0003
Corrugation_RIO:1:C.Data[17] = 0x0000
Corrugation_RIO:1:C.Data[31] = 0x0000


The RA Knowledgebase has Answer ID # 502674 (Access Level: Everyone) that shows the values for these configuration words. From that document:

DSI I/O Config
Sets the number of this channel's drives that are used in Multi-Drive mode. Identifies the connections that would be attempted on a reset or power cycle.
Default: 0 = Drive 0
Values: 0 = Drive 0
1 = Drives 0…1
2 = Drives 0…2
3 = Drives 0…3
4 = Drives 0…4
5 = RTU Master
Type: Read/Write
Reset Required: Yes

The only one that looks wrong is Port 3 on the Slot 1 module, which should be 0x0003 instead of 0x0000.

Be sure to do a reset of the 1769-SM2 or its Adapter to get the Configuration data to be written to the module. It doesn't get sent every I/O scan like the Output data does.
 
Thank you very much Ken!! You're a life saver!
I bet I looked at that about 20 times and could never see that. I'll get it changed and try changing it over again Saturday!
 

Similar Topics

Hello everyone, can anyone help me with covert the STL code to ladder. Iam using plc s71200. A %DB1.DBX33.7 // angel of vaccum...
Replies
2
Views
208
Hello PLCs Forum, I am in a bit of a pickle and was hoping someone could offer me some help. I have a .rss file and just need to see the ladder...
Replies
2
Views
122
Hello nice to meet you, im new in here, I'm currently trying to convert code written in STL for a S7-400 to SCL for an S7-1500, because when i run...
Replies
5
Views
319
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
Replies
3
Views
389
Hello, This will be my first time converting powerflex 40's and 400's from devicenet to ethernet. I did some research, and it seems I will need...
Replies
4
Views
757
Back
Top Bottom