CP341 to Kepware OPC : Modbus TCP
jeffy
Jun 2010
Auckland
35
Hi Modbus experts,
I am currently experiencing ModbusTCP communications trouble.
I want to read Modbus addressed data from a Siemens S7-300 via its CP341 card into my Kepserver OPC using ModbusTCP but I'm unable to establish good comms between the two, and it's starting to drive me nuts now.
CP341 SETTINGS
Slave,
Modbus RTU,
19200,8,1,E
RS485 (two wire half duplex operation)
25blocks of data to be read
Modbus RTU to TCP CONVERTER
Master
Same serial settings as the CP341
Assigned unique IP address on the network
SERIAL CABLE LINK
Terminated as per Siemens CP341 documentation requirements (Two wire half duplex operation) between the CP341 and my Modbus converter unit.
KEPWARE OPC
I can see all other existing (non siemens) Modbus slave devices happily on the network, but cannot see the CP341 only! Kepserver returns an exception code error 0x04 reporting a "Slave device error".
The SF light on the CP341 is clear, so there's no error on it. However the TX and RX green LEDs blink simultaneously every second. I've also used Modbus scan in Step7 to try detect the Master (Modbus RTU to TCP converter unit) but keeps returning an exception error or timeout message as well.
It's probably a simple config issue, but if anyone can bring to my attention anything glaringly obvious that I've missed, will be greatly appreciated!
Thanks guys, any input will be helpful.
Just a comment, but why not use a Kepware OPC server that directly supports Siemens S7 ? Via TCP/IP or MPI or PRofibus ?
Now you want to do this:
S7 Program --> CP341 Modbus RTU Slave interface --> Modbus RTU master/TCP converter --> Kepware Modbus TCP OPC server.
You could have:
S7 Program --> Kepware S7 OPC server.
Will be much more performant, less expensive, easier to configure and more reliable.
Hi i have a cp341 1CH01 Rs485 and et200m ,i wanna use that to interface with a non simense slave device ion7330 are any deference between 1CH02...
1,792
Hi guy 's, can i use cp341 modbus rtu to interface with a non_siemnes slave device , such as schneider ion7330 ?
1,950
Hi, I am using the CP341 for modbus RTU in an ET200 rack. Usually we are using the CP341 for this application in the same central rack as the...
1,060
Hi all, Does anyone have any experience trying to simulate a Modbus master using a PC, The PLC is a cpu 300 with a CP341 RS485. I am...
2,667
Hi, I had RS485 ASCII string going into a CP340 @ 9600baud rate. This was working fine. I had to change my baud rate to 19200 so I got ripped...
2,524