I have a simatic manager installed in my PG. I want to backup the program from CPU 315-2 DP/PN but I do not have the procedure. Still a newbie.
Question:
1. Is there a procedure how to upload the program from PLC to the PG?
2. Do I need to do hwconfig first in simatic manager to upload the program?
3. How do I communicate to the PLC using the interface cable?
4. What version of simatic manager should I use?
Thanks.:confused:
You don't have to do a HW Configuration.
What you have to do is:
- Create a new file
- Set your PG/PC Interface, in your case you could use Ethernet communication.
- Make sure that your ethernet adapter is configured
- Then you can upload your program
It is called "Upload Station to PG".
In the upload dialog you will be prompted for Rack, Slot and IP address.
For an S7-300 set Rack=0 and Slot=2.
You can either enter the IP manually, or search for it via the dialog.
The IP and Subnet of your PLC must be reachable from your PC.
- Create a new file
Hi Hagos,
Can I use an MPI cable? Is an ethernet connection same as using a lan cable?
How to configure an ethernet adapter?
Thanks.
Hi Jesper,
So this is like creating a HW config for CPU and I/Os. How can I search for the IP via the dialog?
Thanks.
Hi Hagos,
Thanks.
Connector X1 will support the MPI interface if it is configured in the PLC- if you have a profibus plug on it then chances are you will have to use ethernet.
Configure the ethernet connection under the Set PG/PC Interface then when you upload in the HWConfig it will ask for a direct IP address or you can have it list available addesses.
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
168
I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
29
747
Hi We were having a few power cuts and the CPU would not work. I had to reset the memory and he CPU would read from the memory card and start...
3,163
Hello everyone... I'm working on a project where I want to use the time of the PLCs to do a specific process. In both PLCs (cpu 224 & cpu 315)...
4,336
Hi, Can anyone explain the difference between rebooting a Siemens CPU 315-2 PN/DP, either by setting the switch into stop and back into run...
2,684