CPU 90-30 GE fault..
sultanahmed
Jul 2013
home
63
Dear All,
I am working on Ge 90-30 system CPU specification is ic693cpu331. Software "PME8.5" i download program.after few days it goes on fault. fault picture is attached as file name "paint1" and "paint"
but when i clear diagnostic table and download program again i get this error.
"Error 8544: Flash operation failed [ Controller Error: Controller Error - Data stored on device has been corrupted and is no longer reliable or the device is not present [0x05][0xCC] ]"
where as when i run cpu all system is working perecftly.
i tried to find this error but unable to find.please help
The column labeled "LOC" identifies which module generated the fault.
0.3 points to the IC693CMM311 module in rack 0, slot 3. The fault itself indicates that the module loses backplane communications with the CPU. It could be a problem with the module or the backplane.
1.7 points to the IC693MDL940 module in rack 1, slot 7. I suggest swapping the modules in slot 6 and 7 to see if the problem follows the module or stays with the slot.
For the Error 8544, uncheck the "Save to flash" box before attempting download. The CPU331 requires a separate EEPROM chip for non-volatile memory. Unless your CPU has one installed you will continue to get the error every time you download.
hello at work we have a machine controlled with an SLC 500 fixed, model 1747-l30c at fault, i plan to migrate to a micrologix controller. I'm...
3,025
Hello everyone, I got called down to a plant to service a powdered metal press. It has an SLC 500 5/02 CPU that was faulted for the code 0002h...
1,815
Hello intelligent people, I hope you guys can help me I currently have a problem with a telemecanique TSX 17 plc The plc was cut off power supply...
2,813
We bought a used SLC500 (1747-l40A) from a vendor. Comes with one year warranty. It's still on our test bench. I downloaded a program to it and...
21
4,216
Hello guys. CPU showed major fault indication.what could be reason. Kindly help and guide to solve the issue. Kind regards.
1,356